    Lately, i have been measuring voltage on the top of combo Run Capacitors that far exceed the voltage rating stamped on the Run Capacitor furnished with the Goodman A/C unit.

    IE: Todays measurement :
    Goodman 2 ton model CK24 unit . Rating of combo run capacitor : 370 v. Voltage as measured on top between common and Herm : 389 v. Unit was operating correctly and incoming voltage entering and leaving the Contactor was 245 v.

    Over the last few weeks, ive measured even greater variances on Goodman A/C Combo Run Capacitors between common and Herm as well as common and fan .How come they didnt put in 440 v. rated Combo Run Capacitors ?? Ive also had quite a few Combo Run Capacitors blow over the last few years on Goodman ... most likely due to the higher voltage imposed on them , than what the rating is.

    Anyone else running into this ?

    Dave

  2. #2
    Join Date
    Jun 2001
    Location
    Tx
    Posts
    3,917
    Post Likes
    Anyone else running into this ? Yes

    I usually go ahead and grab a 35/5 440 off of the truck.

  3. #3
    Join Date
    May 2004
    Posts
    343
    Post Likes
    Thread Starter
    How can a Manufacturer not pick this up in their R&D ??

    RoboTec..if youre still with Goodman, whats your take on this problem ???

  4. #4
    Join Date
    Sep 2001
    Location
    angola indiana
    Posts
    528
    Post Likes

    run caps

    I too have replaced many,many run caps on goodman condensers. I always repcace with 440 .

  5. #5
    Join Date
    May 2004
    Posts
    343
    Post Likes
    Thread Starter
    Thats what i do also.

  6. #6
    Join Date
    Jan 2004
    Location
    Midlothian, Virginia
    Posts
    195
    Post Likes

    how?

    if a capacitor can be thought of as a balloon and voltage a pressure. (electrical pressure that is) how can what you guys see occuring happen. the balloon ( capaacitor in this case) can't have higher pressure than the thing pumping it up. (the line voltage in this case)
    Goodbyee stranger it's been nice. Hope you find your paradise! Hey it aint rocket science, "It's a Trade !"

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes

    The voltage across the cap is from the start winding, not the line voltage.


  8. #8
    Join Date
    Jun 2003
    Location
    Hell Hole Swamp
    Posts
    4,255
    Post Likes
    The caps blowing up is a GE problem, they do this on every manufacturers unit in which they are installed, not just Goodman, the compressor manufacturer specs the run caps anyway

  9. #9
    Join Date
    May 2004
    Posts
    343
    Post Likes
    Thread Starter
    'The caps blowing up is a GE problem, they do this on every manufacturers unit in which they are installed, not just Goodman, the compressor manufacturer specs the run caps anywa
    '

    ME: Not just GE caps either ; have found other brand caps where the voltage on them are considerably above the rating. Youd think these residental Compressor Mfg'rs would just go with all 440 v. rated caps, and be done with it.

  10. #10
    Join Date
    Feb 2005
    Location
    GEORGIA
    Posts
    1,532
    Post Likes
    Oh, beenthere...
    You could take most of "us" back to school..
    This is very much understood...
    Thanks
    Peace,
    Stephen
    "Value our Differences"

  11. #11
    Join Date
    Jan 2004
    Location
    Midlothian, Virginia
    Posts
    195
    Post Likes

    ok the voltage across the start winding is the voltage across the start capacitor.
    and guess what the voltage across the start winding is the line voltage.
    Goodbyee stranger it's been nice. Hope you find your paradise! Hey it aint rocket science, "It's a Trade !"

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Not quite, but close.

    All motors are generators, and all generators are motors.

    The voltage from the start winding is an EMB, with is higher then the line voltage.

  13. #13
    Join Date
    May 2004
    Posts
    343
    Post Likes
    Thread Starter
    Correct. A motor is like a generator in that it generates higher voltage known as BEMF or Back Electromotive Force ; This increased generated voltage comes thru the start winding and thru the wire leading to the Run Capacitor terminal . The other terminal on the RUn Capacitor is for the Run winding on the compressor (or fan motor...as the case may be). The rating of a Run Capacitor , such as 370 volts...must not be exceeded during operation. Its common to find Goodman A/C units all the time where the imposed BEMF voltage is higher than 370 volts. I think the highest ive ever found was over 400 volts .


  14. #14
    Join Date
    Feb 2004
    Location
    Pacific NW
    Posts
    879
    Post Likes
    Never ceases to amaze me how many hvac techs have a total misunderstanding of ac power, and how incorrect opinions are foisted off as wisdom, must be a gross error in some hvac text somewhere? .

    FWIW:
    1. good news - everyone is correct in that the caps should be rated at 440 Vac for good reliability.
    2. bad news - not a single poster seems to understand ac power flow. The 389 or 400 V across the cap IS NOT generated by the start or run winding. The voltage across the cap plus the voltage across the run winding is exactly equal to the line voltage at EVERY specific point in time. When you hook up your digital voltmeter, you are probably reading 1.11 time the average voltage ( any cheap meter, even a Fluke 77 reads 1.1 times average vs true rms). If you hook up a scope (e.g. Fluke 123 or equivalent) across the cap and run winding, you would see that at times the volts of the sine wave across the cap is negative and across the winding is positive and both are higher peaks and rms than line voltage - read up about leading and lagging currents in capacitors and inductors before blathering about back emf, etc. and about resonance and voltage amplification thru resonance, etc. etc.


    [Edited by junkhound on 06-30-2005 at 12:23 AM]

  15. #15
    Join Date
    Jun 2005
    Posts
    347
    Post Likes

    Smile

    I found one today on a no a/c call that had blown apart like one of those magic worms you light a capsul and it grows in to an ash worm. Happy forth of july...

  16. #16
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Junkhound, do yourself a favor. Before blasting people here over giving incorrect information, try researching some about how AC motors work, because you are dead wrong.

    Back EMF is real, and the other posters are correct. In an induction motor with a run and start winding, there is an induced voltage potential between the run and start windings that exeeds the input voltage to the motor.
    This is the same voltage that energizes the coil of a potential relay for a start kit, and is the voltage the capacitor must have a higher rating than.

    http://cougar.slvhs.slv.k12.ca.us/~p...s/backemf.html

    http://www.answers.com/topic/back-emf

    http://www.newton.dep.anl.gov/askasc...0/phy00351.htm

    http://www.chilternweb.co.uk/physics/emag/backe.html

    http://www.4qd.co.uk/fea/pmm.html

    http://www.madsci.org/posts/archives...5941.Eg.r.html



    [Edited by mark beiser on 06-30-2005 at 01:16 AM]

  17. #17
    Join Date
    Jun 2005
    Posts
    1
    Post Likes
    The voltage you are reading is generated accross the start winding called back emf

    [Edited by molabearair on 06-30-2005 at 01:58 AM]

  18. #18
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    You posted some nice links Mark.

    Hopefully others go and read them.

  19. #19
    Join Date
    Feb 2004
    Location
    Pacific NW
    Posts
    879
    Post Likes
    how AC motors work......original comment holds.

    1. never said there was no such thing as back emf, but that is not what causes capacitor voltage higher than line voltage. A cap and inductor of any type (not even a motor) can give higher voltages across the cap than line voltage.....

    2. interesting how a bunch of internet links can be re-interpreted to suit preconceived notions.

    Hook up a 4 channel scope to a motor and them come back and make comments.

  20. #20
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Junkhound, the links were just random Google stuff. Your origonal comment is still wrong.
    I have plenty of hard copy text here, I'll see if I can find something to link that is more relevent to PSC motors when I get home tonight.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •