Results 1 to 8 of 8
  1. #1
    This central air unit was installed with new Lennox G51 furnace in December. Had to wait for the warm weather to test air. This untit has a hard start up, sounding like a electrical surge in the basement where the lines come in. Outside, in addition to the fan noise, a buzzing noise can be heard. This sound radiates inside into the basement and is louder down there. The contractor seems to think it is normal. I say no way.

    Any help out there?

    Thanks

  2. #2
    Join Date
    Mar 2005
    Location
    Suppy NC
    Posts
    4,509
    lenox had a run of realy weak contactors for a while and they would buzzz like a hurd of bees comeing through
    may ask then to check it out

  3. #3
    Thanks, T.

    In lay mans terms, what are the contactors? If this is the problem, do they replace?

  4. #4
    Join Date
    Jan 2004
    Posts
    144
    A contactor is similar to a relay. It uses a low voltage signal (usually from the thermostat calling for cooling) to power an electro-magnet; this magnet then pulls in a heavy set of electrical contacts. These contacts then route the high voltage power to the compressor and condenser fan.
    That being said, call your HVAC contractor to have this checked and replaced. If it is buzzing on a new unit then the electro-magnet coil is weak and should be replaced. The HS26 is one of the quieter units, and that is one of their big selling points - don't let your installer shine you on.
    ****** CAUTION THE CONTACTOR IS A HIGH VOLTAGE DEVICE, DO NOT REPLACE THIS YOUR SELF. THIS IS NOT A DIY PROJECT, ******
    Licensing laws are tough, and it's about time.

  5. #5
    mam123-Thanks for the reply..now I am starting to understand.

    Trust me, I would never attempt this on my own. Just my contractor.


    Would this explain the hard "high voltage" sounding surge start-ups? And would this warrant asking for a new unit or can this be fixed with no later break downs?

  6. #6
    Join Date
    Mar 2002
    Location
    Richmond, Virginia
    Posts
    4,264
    Could you post the entire HS29 model number? The HS29-018 (1-1/2 ton condenser) has a reciprocating compressor. HS029-024- HS29-060 has a scroll. If it's 1-1/2 ton and they installed an evaporator equipped with a TXV, the condenser will need a hard start kit.

    The problem is likely just the contactor however. That unit has a 5 year parts warranty from Lennox. Insist that the problem gets resolved.
    There is nothing more frightful than ignorance in action....Mark Twain

  7. #7
    HVAC PRO-

    Thanks for your reply. It is a 2 ton. HS29-024.

    Do you think the contractor can fix without replacing the entire unit?

  8. #8
    Join Date
    Nov 2001
    Posts
    1,874
    Just call your installation company,
    They can answere the questions you have,while they fix your unit in minutes.
    If you try to fail, and succeed.
    Which have you done ?



Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event