    Help with charging

    New walk in cooler for a liquor store.

    Customer provided equipment.

    Four 5200 btu evaporators with TXV.

    R-404a

    Condensing unit: Copeland FJAM-A300-TFC-020 with fan cycling for head pressure control.

    135 feet of line set mostly 1 1/8 and 5/8.

    Receiver capacity is 10.3 pounds. The rep could not tell me if it was 90% capacity or full. Receiver is Blissfield B0600012VR-140.

    Rep advised me to charge to a clear sight glass. I want to shoot for 12 degrees Subcooling, but don't want to overcharge and have problems when it pumps down on it's off cycle.

    I also want to set about 8 degrees superheat on each of the four TXVs. I can take the line temperature close to the buld, but don't have good access to and suction line taps. Is it okay to use the suction pressure reading at the condensing unit 135 feet away to figure superheat?
    Beware of advice given by some guy on the Internet.

  2. #2
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    666

    Lightbulb

    Milk man - You can't charge a system with a receiver with sub coolong , it is what it is..
    Charge to a full sight glass and and add 10% then pump down watch high side needle for rise over 5 psi if it does you are over charged if it does not run torch up and down receiver a couple of passes then take your finger and run it up receiver where the temp changes from cool to hot is your liquid level, Not To Exceed 80% volume,.... You are now charged...


    Hope this Helps...
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,951
    Agree. Forget about subcooling. Clear the glass.

    Now, are you certain there isn't a headmaster hidden behind the receiver? What is the lowest ambient where you are? Fan cycling is really a poor method for low ambient control. Where is the LLSV?

    If you have a headmaster, following Sporlan's 90-30-1 charging guidelines are the BEST way to ensure proper charge over all conditions.

    As far as superheat, I'd check the pressure at the evaps if possible. If not, add a pound or two and use the reading from the unit. You'll be OK.

  4. #4
    Join Date
    May 2010
    Posts
    1,289
    Headmasters... Pain in my asssss

  5. #5
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    666

    Talking

    About to change one in about 20 minutes ....Warranty Manitowoc
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  6. #6
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,951
    Quote Originally Posted by ZeroTolerance View Post
    Headmasters... Pain in my asssss
    Live where it is very cold and you'll change your tune.....

  7. #7
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,157
    my biggest issue with headmasters WAS my ignorance on how they work .. once it soaked in I prefer them over fcc any day of the week

  8. #8
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    5,895
    Quote Originally Posted by jpsmith1cm View Post
    Live where it is very cold and you'll change your tune.....
    Ditto on that!!!
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  9. #9
    Join Date
    Jun 2005
    Location
    Las Vegas NV
    Posts
    1,111
    See below
    Last edited by powell; 03-30-2011 at 04:08 PM. Reason: duplicated myself

  10. #10
    Join Date
    Jun 2005
    Location
    Las Vegas NV
    Posts
    1,111
    Quote Originally Posted by Milk man View Post
    Condensing unit: Copeland FJAM-A300-TFC-020 with fan cycling for head pressure control. This model did not come from Copeland with a FCC. If it has one then it was installed by others.

    135 feet of line set mostly 1 1/8 and 5/8. the liquid line is too big, 1/2" would be the optimum size.

    Receiver capacity is 10.3 pounds. The pump down capacity of the receiver that Copeland used is 16.3 lbs. It must have been changed or the rep was incorrect.
    powell

  11. #11
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    7,972
    Thanks to all. Will take everyone's advice.
    Beware of advice given by some guy on the Internet.

  12. #12
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    7,972
    Quote Originally Posted by jpsmith1cm View Post
    Agree. Forget about subcooling. Clear the glass.

    Now, are you certain there isn't a headmaster hidden behind the receiver? What is the lowest ambient where you are? Fan cycling is really a poor method for low ambient control. Where is the LLSV?

    If you have a headmaster, following Sporlan's 90-30-1 charging guidelines are the BEST way to ensure proper charge over all conditions.

    As far as superheat, I'd check the pressure at the evaps if possible. If not, add a pound or two and use the reading from the unit. You'll be OK.
    I didn't see one but assumed there was one. I called the leed man this morning and he told me no on the headmaster and it is set up for fan cycling.

    We can expect zero degrees for a few days each winter.

    LLSV in cooler just before the first evaporator.
    Beware of advice given by some guy on the Internet.

  13. #13
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    666

    Lightbulb

    Great call Powell I was in a zone when I answered this morning , It didn't look right then, and started to get busy so I just answered his question.... But great call...