Help with charging
New walk in cooler for a liquor store.
Customer provided equipment.
Four 5200 btu evaporators with TXV.
R-404a
Condensing unit: Copeland FJAM-A300-TFC-020 with fan cycling for head pressure control.
135 feet of line set mostly 1 1/8 and 5/8.
Receiver capacity is 10.3 pounds. The rep could not tell me if it was 90% capacity or full. Receiver is Blissfield B0600012VR-140.
Rep advised me to charge to a clear sight glass. I want to shoot for 12 degrees Subcooling, but don't want to overcharge and have problems when it pumps down on it's off cycle.
I also want to set about 8 degrees superheat on each of the four TXVs. I can take the line temperature close to the buld, but don't have good access to and suction line taps. Is it okay to use the suction pressure reading at the condensing unit 135 feet away to figure superheat?Beware of advice given by some guy on the Internet.
-
03-30-2011, 09:04 AM #2
Milk man - You can't charge a system with a receiver with sub coolong , it is what it is..
Charge to a full sight glass and and add 10% then pump down watch high side needle for rise over 5 psi if it does you are over charged if it does not run torch up and down receiver a couple of passes then take your finger and run it up receiver where the temp changes from cool to hot is your liquid level, Not To Exceed 80% volume,.... You are now charged...
Hope this Helps...Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!
-
03-30-2011, 11:11 AM #3
Agree. Forget about subcooling. Clear the glass.
Now, are you certain there isn't a headmaster hidden behind the receiver? What is the lowest ambient where you are? Fan cycling is really a poor method for low ambient control. Where is the LLSV?
If you have a headmaster, following Sporlan's 90-30-1 charging guidelines are the BEST way to ensure proper charge over all conditions.
As far as superheat, I'd check the pressure at the evaps if possible. If not, add a pound or two and use the reading from the unit. You'll be OK.
-
03-30-2011, 11:41 AM #4
Regular Guest
- Join Date
- May 2010
- Posts
- 1,289
Headmasters... Pain in my asssss
-
03-30-2011, 12:27 PM #5
About to change one in about 20 minutes ....Warranty Manitowoc
Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!
-
03-30-2011, 01:17 PM #6
-
03-30-2011, 01:43 PM #7
my biggest issue with headmasters WAS my ignorance on how they work .. once it soaked in I prefer them over fcc any day of the week
-
03-30-2011, 02:58 PM #8
-
03-30-2011, 04:05 PM #9
Professional Member*
- Join Date
- Jun 2005
- Location
- Las Vegas NV
- Posts
- 1,111
See below
Last edited by powell; 03-30-2011 at 04:08 PM. Reason: duplicated myself
-
03-30-2011, 04:07 PM #10
Professional Member*
- Join Date
- Jun 2005
- Location
- Las Vegas NV
- Posts
- 1,111
-
03-30-2011, 06:31 PM #11
Professional Member*
- Join Date
- Nov 2001
- Location
- east kansas
- Posts
- 7,972
Thanks to all. Will take everyone's advice.
Beware of advice given by some guy on the Internet.
-
03-30-2011, 06:35 PM #12
Professional Member*
- Join Date
- Nov 2001
- Location
- east kansas
- Posts
- 7,972
Beware of advice given by some guy on the Internet.
-
03-30-2011, 06:41 PM #13
Great call Powell I was in a zone when I answered this morning , It didn't look right then, and started to get busy so I just answered his question.... But great call...
Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!


Reply With Quote