Thread: Sizing question
-
06-26-2005, 12:33 PM #1
Regular Guest
- Join Date
- Jul 2004
- Location
- Indiana
- Posts
- 27
2200 SQ FT 10FT CEILINGS BROTHER IN LAWS 3 TON CONDENSER CAN ONLY GET TEMP TO 77 WHEN T-STAT CALLS FOR 69 AND COMPRESSOR THERMAL O/LSs After 45 minutes or so kicks on (Compressor).
Again this is only when ambient is 90+. Would a larger condenser and A coil HELP THIS Delima..? wHEN IT COOLING REGISTER AIR IS 64 DEG
CAP. TUBE
AMBIENT 89
LIQUID L PSI 228
TEMP LIQ LINE 90
iNDOOR WB 64
SUCTION PSI 70
SUCTION LINE TEMP 75 AND SWEATING
CALCULATED 10 DEGRES SUPERHEAT + OR -5 DEGREES
GOD BLESS ARE VETERANS Living and Deceased so we can practice our PROFESSION HAVE A PROFITABLE DAY
-
06-26-2005, 12:40 PM #2
do manul j and see what it calls for
-
06-26-2005, 12:43 PM #3
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,351
Undersized & Underperforming Combo?
BOTH Undersized and Underperforming:Originally posted by fatcat
2200 SQ FT
10 FT CEILINGS
3 TON CONDENSER, 77'
When it is COOLING REGISTER AIR is 64'
___Underperforming based on 13'F Delta T air flow.
___Seems significantly __Undersized (needs At Least 4-ton or maybe even a 5-ton) based on my experience performing ACCA Manual J 8th edition analysis on 300+ custom homes.
However, you have not provided:
1. R-values for Walls
2. R-value of Ceiling
3. Window Area
(including Sliding glass doors) on EACH Side of house
4. Windows CLEAR or Tinted
5. House Orientation
MORE Later in Update or Follow-up
[Edited by dan sw fl on 06-26-2005 at 12:54 PM]Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
06-26-2005, 12:52 PM #4
First thing to do is find out why comp won't stay running. Undersized unit working properly can run 24/7 without failing. You say register air only 64. Also take readings of supply & return right at the unit and see if you are picking up considerable duct heat gain.
-
06-26-2005, 12:52 PM #5
I think you had better find out why it is overloading and i think the house will cool better!
Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced
-
06-26-2005, 01:19 PM #6
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,351
Calc by Aprpox. Manual J Method
Summary of Approx. Loads
.......WINDOWS.. 15,444 BTUh CLEAR GLASS 280 S.F.
.......CEILING.. 6,368 R-19
.........Walls.. 2,292 R-19
.........Floor....... 0
.........DUCT.....6,286 R-6 in 130'F Attic
.INFILTRATION.....2,420
.INTERNAL Gains...2,977
.........People...1,466
_________TOTAL___37,153. BTUh = 4-Ton
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
06-26-2005, 01:39 PM #7
Professional Member
- Join Date
- Jul 2004
- Location
- midwest
- Posts
- 2,868
Dan, I know everything your doing is trying to help but why give these loads without knowing the needed info. There is most likely a contractor that is trying to fix this and you giving incorrect information will only make matters worse. His first problem is getting the unit working like it should and then he can see if there is a size problem.
-
06-26-2005, 01:48 PM #8
I hope that suction line temp of 75° was a type o, error.
70 psi is a saturation temp of 41°, that would give you 34° superheat.
-
06-26-2005, 01:49 PM #9Originally posted by beenthere
I hope that suction line temp of 75° was a type o, error.
70 psi is a saturation temp of 41°, that would give you 34° superheat.
Which would explain the compressor going out on over load.
-
06-26-2005, 02:04 PM #10
Professional Member
- Join Date
- Feb 2003
- Posts
- 538
Assuming your readings are right it appears overcharge w/ a restriction
-
06-26-2005, 02:47 PM #11
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,351
Parallel Path Processing
Following PARALLEL SIZING & Performance PathsOriginally posted by trane
His first problem is getting the unit working like it should and then he can see if there is a size problem.
is a COMPLETELY ROUTINE Evaluation Process
which requires a couple iterations.
DEVELOP THE WHOLE PICTURE.
If you can't stand the heat, get out of the kitchen.
Fatcat,
It is QUITE OBVIOUS within < 7-minute evaluation that
75'F will never be consistently achieved at Outside Design Temperature with a Good performing 3-ton unit, UNLESS there are < 130 S.F. TOTAL AREA of Tinted windows in this 2,200 S.F. house.
NEARLY ALL (i.e. 97%) U.S. HOUSES
HAVE > 10% RATIO OF GLASS-TO-FLOOR AREA.
I'd say __< 1% chance__ of this 3-ton being the most appropriately sized unit in this case.Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
06-26-2005, 03:04 PM #12
Professional Member
- Join Date
- Jul 2004
- Location
- midwest
- Posts
- 2,868
Re: Parallel Path Processing
Or the 2200 sq. ft. includes a basement, earth contact home, foam and concrete walls, foam insulation, the list goes on. If it was a home that I had sized I wouldn't want someone guessing on the internet and telling the homeowner I had installed the wrong size. I hope you see my point.Originally posted by dan sw fl
Following PARALLEL SIZING & Performance PathsOriginally posted by trane
His first problem is getting the unit working like it should and then he can see if there is a size problem.
is a COMPLETELY ROUTINE Evaluation Process
which requires a couple iterations.
DEVELOP THE WHOLE PICTURE.
If you can't stand the heat, get out of the kitchen.
Fatcat,
It is QUITE OBVIOUS within < 7-minute evaluation that
75'F will never be consistently achieved at Outside Design Temperature with a Good performing 3-ton unit, UNLESS there are < 130 S.F. TOTAL AREA of Tinted windows in this 2,200 S.F. house.
NEARLY ALL (i.e. 97%) U.S. HOUSES
HAVE > 10% RATIO OF GLASS-TO-FLOOR AREA.
I'd say __< 1% chance__ of this 3-ton being the most appropriately sized unit in this case.


Reply With Quote