I have a problem that I cant figure.The suction line is in a vacuum as soon as the unit starts.I thought it must be low on refrigerant so I leak checked unit.Could not find anything,so I recovered the charge,weighed it and it was ok.I weighed in the correct amount again,and the suction goes into a vacuum again.(R-22 unit by the way)The nameplate says 11.7 amps and it draws only 5+The lineset isnt too long.It is a 110 volt unit.All the fans work.It is a Heat Controller model A-HMC12AS.Any thoughts or suggestions out there?I would really appreciate it.
-
06-25-2005, 05:42 PM #2
restriction and or bad txv
-
06-26-2005, 02:37 AM #3
Professional Member*
- Join Date
- Mar 2002
- Location
- Concord, CA
- Posts
- 2,628
Just one: Call a professional. No offense intended. But tinknocker's answer could have been provided by a recent trade school graduate, which means you should have been able to provide it as well.Originally posted by mark7
Any thoughts or suggestions out there?
-
06-26-2005, 02:50 AM #4
Professional Member
- Join Date
- Nov 2004
- Posts
- 2,923
Or,open the liquid service valve.Originally posted by mark7
Any thoughts or suggestions out there?I would really appreciate it.
(but dont mention this to Irascible...)
-
06-26-2005, 03:17 AM #5
Professional Member*
- Join Date
- Mar 2002
- Location
- Concord, CA
- Posts
- 2,628
-
06-27-2005, 09:49 AM #6
Regular Guest
- Join Date
- Sep 2003
- Posts
- 86
I should of mentioned I checked the service valves.They are open.There isnt a expansion valve,it is a fixed orifice.Any other suggestions?
-
06-27-2005, 11:24 AM #7
Regular Guest
- Join Date
- Aug 2004
- Location
- west hartford, ct
- Posts
- 74
Did you forget to take the rubber plug out of the lines set before making connections. I have seen this before.