Results 1 to 7 of 7

Hybrid View

  1. #1
    Join Date
    Sep 2003
    Posts
    86
    Post Likes
    I have a problem that I cant figure.The suction line is in a vacuum as soon as the unit starts.I thought it must be low on refrigerant so I leak checked unit.Could not find anything,so I recovered the charge,weighed it and it was ok.I weighed in the correct amount again,and the suction goes into a vacuum again.(R-22 unit by the way)The nameplate says 11.7 amps and it draws only 5+The lineset isnt too long.It is a 110 volt unit.All the fans work.It is a Heat Controller model A-HMC12AS.Any thoughts or suggestions out there?I would really appreciate it.

  2. #2
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    restriction and or bad txv

  3. #3
    Join Date
    Mar 2002
    Location
    Concord, CA
    Posts
    2,715
    Post Likes
    Originally posted by mark7
    Any thoughts or suggestions out there?
    Just one: Call a professional. No offense intended. But tinknocker's answer could have been provided by a recent trade school graduate, which means you should have been able to provide it as well.

  4. #4
    Join Date
    Nov 2004
    Posts
    2,928
    Post Likes
    Originally posted by mark7
    Any thoughts or suggestions out there?I would really appreciate it.
    Or,open the liquid service valve.

    (but dont mention this to Irascible...)

  5. #5
    Join Date
    Mar 2002
    Location
    Concord, CA
    Posts
    2,715
    Post Likes

  6. #6
    Join Date
    Sep 2003
    Posts
    86
    Post Likes
    Thread Starter
    I should of mentioned I checked the service valves.They are open.There isnt a expansion valve,it is a fixed orifice.Any other suggestions?

  7. #7
    Join Date
    Aug 2004
    Location
    west hartford, ct
    Posts
    74
    Post Likes
    Did you forget to take the rubber plug out of the lines set before making connections. I have seen this before.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.