    I have a brand new house in tampa florida. 1995 sq. ft. I have a 3 1/2 ton heatpump and a 4 ton air handlerlocated in my garage. My air handler cabinet is sweating and it is not missing any insulation inside the unit. What eles could be causing this condition.

    [Edited by kepner19 on 06-24-2005 at 10:06 PM]

  2. #2
    Join Date
    Jun 2004
    Location
    EXIT 16W www.wmtandson.com
    Posts
    4,822
    Post Likes
    In order for condensation to accur cold air must hit a heated space.... insulaTION prevents condensation. check to see if the airhandler is properly insulatred...
    DON"T mess with the US
    I thought I had been there and done That.
    ITS ALL ABOUT LEARNIN!
    I thought it would be better by now
    "He who works with his hands is a laborer.
    He who works with his hands & his head is a craftsman.
    He who works with his hands, his head & his heart is an artist."
    ~St. Francis of Assisi

  3. #3
    Join Date
    May 2005
    Posts
    428
    Post Likes
    you might bump the speed of the blower motor up one notch and see if that helps.

  4. #4
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    69,738
    Post Likes
    Do not bump the motor speed up. The system is doing what it is designed to be doing.

    In your area, air handlers in unconditioned areas should have added insulation. Get some duct wrap insulation and loosely cover the entire unit. Be sure to seal all seams to seal off the vapor barrier potential of the foil vapor barrier.

    Insulation works off of air spacing between the layers of insulative material. If you pull the insulation tight, you will lose the insulation value.
    ...seek, and ye shall find;..
    So always seek the Truth, not just what you want to believe to be true…
    Ecclesiastes 10:2 NIV


  5. #5
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    4,478
    Post Likes
    Yeah, what robo said.

    If the cabinent is cooler than the webbulb of the air around the unit, it will sweat, like a cold glass of water. Most a/hs in crawls around here sweat one time or another, and I've seen them in attics, knee walls and even indoors sweat.
    Col 3:23


    questions asked, answers received, ignorance abated

  6. #6
    Join Date
    May 2005
    Posts
    428
    Post Likes
    You might call a contractor out to see if the system was adjusted in properly. if not the system will never operate to max performance. if the blower was set at to low of a speed from day one this can cause excessive sweating. the slower the air moves the colder the air on the outlet of the evaperator coil. example put one glass of water on table then put glass of ice water on table which glass is going to sweat the most ? i would try this first .

  7. #7
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Post Likes
    This is common in your area,not normal ,but common.


    Possible reasons;
    1.High return static,pulls water off the coil.Ducts likely undersized.

    2.Improper trap,in condensate line,allows air to be pulled in ,prevents water from draining.

    If you have a zoning system with a bypass,some sweating ,is normal,due to colder coil temperatures.