    ZoneFirst w/ Honeywell thermostat not getting the heat call signal

    A little more than a month ago I had dual zone installed. I have Honeywell thermostats with a ZoneFirst H32P Uni-Zone Master Zone board. The system has worked for a month. However, now when I make a call for heat on the main floor, the Honeywell t-stat is getting the signal, but nothing happens on the Zone First board. When I call for heat on the second floor everything works as expected. Also I have a whole house steam humidifier that is attached to the main floor t-stat. When it calls for humidity, the Zone First board correctly calls for just the fan and opens the correct damper. It just doesn't make any sense why it just stopped working.

  2. #2
    Join Date
    Oct 2015
    Posts
    1
    Post Likes
    Check the dip switches on the board to make sure they are on the proper settings also make sure the board is wired to proper terminals they should correspond with thermostat and dip switches

  3. #3
    Join Date
    Jan 2012
    Location
    Broomall, PA
    Posts
    850
    Post Likes
    Could be something as simple as a loose wire on a terminal, or damaged thermostat wire to the zone board. Check to see if that thermostat wire is continuous (or look for junction box), is broken/damaged/cracked.

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    10,429
    Post Likes
    Please don't guess.
    You need an experienced tech with a meter to find what happened.