Results 1 to 9 of 9
Thread: Trane Voyager
-
03-28-2011, 07:38 PM #1
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,212
Trane Voyager
YCD090C4HOBE
L46103639D
would not lite off, outlet gas pressure, 1st check___-0.33"
ignitor good,draft prior to gas valve opening___-2.65"
after ignition failure, gas valve energizes 2 more times without inducer engaging
could not get gas pressure screwed down any further, it actually would not go below 1.1" on subsequent tries to fire and adjust
ok, bad gas valve
never seen the gas valve engage without inducer before
ok,bad ignition board
here's the clincher of things i've never noticed/seen on voyager, flue passages out the back of HX actually move (spin) when grabbed and shaken
that can't be good
did i miss something here?
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
03-28-2011, 08:38 PM #2
take the top off and check,sounds like bad exchanger.As far as other problem sounds like ignition board.
work to live not live to work.
-
03-28-2011, 08:45 PM #3
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,212
I had the top off, generally don't miss the opportunity to condemn a choo-choo
no physical holes found, just those loose tube on the back of HX
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
03-29-2011, 06:51 AM #4
Professional Member
- Join Date
- Mar 2010
- Location
- Va.
- Posts
- 178
You can't get a good gas pressure reading with the inducer fan off. Did you check for voltage at the inducer motor when the gas valve energizes?
-
03-29-2011, 09:56 PM #5
Professional Member
- Join Date
- Jun 2008
- Location
- NY
- Posts
- 33
You may have a bad inducer motor or like Local 553 said a bad board. Those are 2 speed motors on that unit. I had a 5ton unit several years back that would not fire. All my readings were perfect. Turned out a spider made a web in the oriface on the inside of the air intake plate. Cleaned it out and all worked fine. Good luck
-
03-30-2011, 06:26 AM #6
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,212
inducer not powering up those last 2 times before lock out, just gas valve.
have had bad ignition boards before, but not same symptoms
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
01-26-2013, 09:53 AM #7
New Guest
- Join Date
- Jan 2013
- Posts
- 1
This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.
You can find the rules for posting and qualifications here.
Additional infractions may result in loss of posting privileges.
Last edited by jpsmith1cm; 01-27-2013 at 09:25 AM. Reason: Non AOP member
-
01-27-2013, 09:26 AM #8
Serviceman777
This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.
You can find the rules for posting and qualifications here.
Additional infractions may result in loss of posting privileges.
-
01-27-2013, 03:27 PM #9
Additional note to New Guests:
PLEASE do not dig up old threads just so you can post your "solution" or your "two cents."
If you are a regular member and want to meet the requirements for Professional Member, it's a good idea to take part in CURRENT threads in the tech to tech open area. NOT in the AOP.
So, there is no reason to dredge up threads from long ago......
And ONLY post in AOP if you have read the requirements for that section, and you meet one of the two category requirements for making a post there.
This will make things a lot easier. Thanks.[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:


Reply With Quote