Results 1 to 9 of 9
Thread: Trane Voyager
    Trane Voyager
    YCD090C4HOBE
    L46103639D
    would not lite off, outlet gas pressure, 1st check___-0.33"
    ignitor good,draft prior to gas valve opening___-2.65"
    after ignition failure, gas valve energizes 2 more times without inducer engaging
    could not get gas pressure screwed down any further, it actually would not go below 1.1" on subsequent tries to fire and adjust
    ok, bad gas valve
    never seen the gas valve engage without inducer before
    ok,bad ignition board
    here's the clincher of things i've never noticed/seen on voyager, flue passages out the back of HX actually move (spin) when grabbed and shaken
    that can't be good
    did i miss something here?
    Mar 2009
    central illinois
    take the top off and check,sounds like bad exchanger.As far as other problem sounds like ignition board.
    work to live not live to work.
    I had the top off, generally don't miss the opportunity to condemn a choo-choo
    no physical holes found, just those loose tube on the back of HX
    Mar 2010
    Va.
    You can't get a good gas pressure reading with the inducer fan off. Did you check for voltage at the inducer motor when the gas valve energizes?
    Jun 2008
    NY
    You may have a bad inducer motor or like Local 553 said a bad board. Those are 2 speed motors on that unit. I had a 5ton unit several years back that would not fire. All my readings were perfect. Turned out a spider made a web in the oriface on the inside of the air intake plate. Cleaned it out and all worked fine. Good luck
    inducer not powering up those last 2 times before lock out, just gas valve.
    have had bad ignition boards before, but not same symptoms
    Jan 2013
    Serviceman777
    Southeastern Pa
    Additional note to New Guests:
    PLEASE do not dig up old threads just so you can post your "solution" or your "two cents."
    If you are a regular member and want to meet the requirements for Professional Member, it's a good idea to take part in CURRENT threads in the tech to tech open area. NOT in the AOP.
    So, there is no reason to dredge up threads from long ago......
    And ONLY post in AOP if you have read the requirements for that section, and you meet one of the two category requirements for making a post there.
    This will make things a lot easier. Thanks.
    2 Tim 3:16-17
    AOP Forum Rules:
