HVAC guy still here and cannot get the air handler on zone system to shut off even when new board and the thermostats are disconnected. Any idea?
-
06-24-2005, 02:46 PM #2
Regular Guest
- Join Date
- Jul 2000
- Location
- Columbia, SC. USA
- Posts
- 1,143
Blower relay or blower board bad...? Is someone looking over my shoulder?!?!
-
06-24-2005, 02:56 PM #3
Professional Member
- Join Date
- Apr 2005
- Location
- Richmond, Virginia
- Posts
- 365
Give the guy a break. It's a short between R and G.
Disconnect R and G from unit and ohm out until you find short.Sean Cantrell
-
06-24-2005, 06:38 PM #4
If he disconnects the green wire from the G terminal, and the fan still runs.
Then if its a heat pump, check to see if the limit is open.
-
06-24-2005, 07:23 PM #5
Find a tech who knows how to troubleshoot a simple low voltage problem, or possibly a stuck contact on a relay
-
06-24-2005, 07:43 PM #6
Regular Guest
- Join Date
- Jun 2005
- Posts
- 4
Turns out there was a small black U shaped wire laying at the botton below the interior board in the unit. Some kind of relay that had fell out. He put both ends of that in and everything works works!
-
06-24-2005, 08:01 PM #7
if it is electric airhandler wigth heaters i think the sequencer is stuck and not turning fan off