    Arrived at job. Lady said, there was a water leak in the bsmt. This renovation comp. came, dug-out and installed new wheeping tiles. While doing that, they disconected the A/C and moved it. Re-connected it after they finished.

    A/C, of course, was not working immediately thereafter.

    So, I put my gauges, and what do I see. S.L. 25psig, L.L. 500 psig (it took only 3-4 seconds to reach 500 psig). Luckily I was fast enough to pull the plug on the 240 V disconnect box. This is Concord 2 ton installed in 2000.

    Oh, I forgot, this renov. comp. actually burried both coper pipes underground.

    Compressor was drawing 9 AMPS (plate says 10.2 AMPS).

    Apparently there is a restriction - the question is where is that ?

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    31,540
    Full of air probably. A restriction would just condense the refrigerant in the outdoor coil and your head wouldn't skyrocket.

  3. #3
    Join Date
    Nov 2004
    Location
    CA
    Posts
    236
    BaldLoonie "...Full of air probably...."


    Well, that's what I though first, but then I decided if the system is full of air - would not the S.L. reading be HIGH too ?

    It is only 25 psig on the S.L.

  4. #4
    Join Date
    Nov 2001
    Location
    Port Saint Lucie, FL
    Posts
    1,582
    I'll take both lines kinked/crushed under the slab for $200 Alex.

  5. #5
    Join Date
    Sep 2004
    Posts
    3,157
    and i will take

    " How does air get into a sealed system " for $100

  6. #6
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    14,903
    Originally posted by bananaboy
    While doing that, they disconected the A/C and moved it. Re-connected it after they finished.
    There is you answer a big old restriction, they should have called an a/c company to take a/c loose and reinstall, when did renovation company's start taking on the liability of removing a/c units?
    “I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay

    The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.

    No Guns…No Freedom…Know Guns…Know Freedom.










Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •