Page 2 of 3 FirstFirst 123 LastLast
Results 14 to 26 of 32
  1. #14
    Join Date
    Jun 2005
    Location
    New York
    Posts
    205
    Post Likes
    I bet you when the tech said it was overcharged by 1 1b, it wasnt an exact figure, that 1 lb if it was, was just to get his readings correct. If the system was off for alittle while, the ducts would be hot giving a higher temp loose from the A/H to the air outlets. There is going to be some increase in temp when the ducts are in a hot location, from the time the air leaves the A/H to the time it exits the air outlets (7 deg is alot). The tech that came out was mostlikly from the installing contractor and is not going to say anything too negitive if the system was undersized. IMO, unless you have a very well insulated home and is some kinda energy eff home, and is sitting under a blanket, I usually (depends) use 400-450 sq ft per ton, sometimes 350 (they used about 700 Sq ft per ton) I am not a big resi guy, and would not be able to to a load calculation for you on the computer. I see your not going to get too much sleep over this. Bring in another HVAC company to help you out. The system may be able, w/ some very fine tweeking, to do alttle better, I dont think so though, it sounds some what small.

  2. #15
    Join Date
    Dec 2002
    Posts
    174
    Post Likes

    what was....

    ....the superheat or subcooling? Ive found noncondensibles in new homes many times. The builders will let their hack installers do start ups and they dont have a clue as to what they are doing. I had one tell me that if he has 70 suction pressure and 250 liquid pressure then he calls it good. Another thing I can tell you about new homes is that the attics are ALWAYS under ventilated. Im amazed at how these so called builders get by with this crap. Oh, and by the way, I bet they used an Allstyle plenum coil and I KNOW they didnt put a drier on the liquid line. Sorry if I sound so negative but I really hate home builders. I equate them with lawyers.

  3. #16
    Join Date
    Sep 2001
    Location
    Vancouver Canada
    Posts
    996
    Post Likes
    Can't comment on whether your system is undersized or not as have no way to see the house from here. Good attic ventilation is worth about 1/2 ton of A/C so if you think you need a bigger unit why not try putting a heat activated roof vent fan in the roof. If the ductwork is not adequatly insulated dropping the temperature in the attic by means of good ventilation will certainly go a long way towards lowering the temperature at the vents. I generally don't like to see temps in excess of 60 degrees at the registers. 54 or 55 would be a far better cooling temp. If things are set up correctly the system should be sized to pull the temp down to 75 degrees on a 90+ degree day. What is temperature during the hottest part of the day in your attic?
    "Go big or Go Home"

  4. #17
    Join Date
    Apr 2004
    Posts
    18
    Post Likes
    I think you said it was 53 % humidity - that can play a big role. Before you can cool the air you need to take the moiture out of the air...speculation...2.5 is a little small - I installed in my own house (1700 sq feet) a 3 ton - 600 sq feet per ton is what I go by - but in more humide areas I would go a little larger to handle the extra load. Do you have a programable stat - if so give the unit somemore run time to help it get an early start on the hot day.

    Good luck

  5. #18
    Join Date
    Jun 2005
    Posts
    37
    Post Likes
    Thread Starter
    Bought a digital themometer at walmart.
    Duct is R-6

    @ 9:42 pm temp at vent in room read 59*

    @ 9:50 return air read 75.6

    Thats a 16.6 degree drop.
    -----------------------

    Return air at plenum(drilling hole and sticking themometer inside) read 76.6

    Plenum out (again drilling hole and sticking theometer inside) read 57.7

    18.9 degree drop
    --------------------------------
    Temp in attic is 90*

    Temp in house with digital themometer at thermostat is 76*


    I need to remind everyone that these are the readings when the a/c actually cools at night

    Now these are the readings when the a/c actually seems to cool.

    I will get readings tommorro when it is HOT!!!

  6. #19
    Join Date
    Jun 2005
    Posts
    37
    Post Likes
    Thread Starter
    here is the link for the floor plan to my house

    http://www.perryhomes.com/inventory/...0%27+Homesites

    just go there and click floor plan and tell me if you think my

    2.5 ton carrier is undersized



    Thanks for everyone's help. I appreciate it

  7. #20
    Join Date
    Sep 2001
    Location
    Vancouver Canada
    Posts
    996
    Post Likes
    What is the r value of the insulation in the attic and walls of your house. ie: 2x6 construction in the walls? R30 in the attic?
    "Go big or Go Home"

  8. #21
    Join Date
    Jun 2005
    Posts
    37
    Post Likes
    Thread Starter
    Black Adder:

    The insulation in the attic is as follows:

    Thermaglass blown in

    The sheet in the attic say's
    ------------------------
    R-30
    attic space 1519 sq feet
    22 bags needed 31 bags used
    min thickness 12"
    Thickness looks around 14" going off their markers and looking all over attic

    For the walls I can't tell you what they used

  9. #22
    Join Date
    Apr 2003
    Location
    California
    Posts
    634
    Post Likes
    call the registar of contractors to help you before it is to late. builders love to save money on ac systems....

  10. #23
    Join Date
    Jun 2005
    Posts
    37
    Post Likes
    Thread Starter
    Whats the registar of contracters?

    How do I get hold of them?

  11. #24
    Join Date
    Jun 2005
    Posts
    37
    Post Likes
    Thread Starter
    tech is coming over today. I will have to let everyone know what he say's.

  12. #25
    Join Date
    Jun 2005
    Posts
    37
    Post Likes
    Thread Starter
    Tech said he had to add a little freon this time. Said he took out too much.

    My conclusion to the whole mess
    --------------------------------------
    The AC unit is working properly
    Temp @ Plenum return 79.2*
    Temp @ Plenum out 59.9*
    (Thats a difference of 20.4*)

    Attic Temp 134.4*

    Temp at vent with longest run 66.6*
    (Thats a loss of 7 degree's)

    Return air temp 75*
    (Thats a loss of 4.2 degree's)

    All duct is R-6 and insulation in attic is R-22 with and adv of 14 inches loose fill

    What are your thoughts of increasing preformance so the a/c doesn't have to run all day?
    --------------------------------------------------------
    1.)Increase R-value of return air and other ducts?
    - it would be a pain for me the diy to do.

    2.) Put in powered ventilation either gable or roof mount
    - I am afraid if I put in powered roof mount it will just suck air in from the other vents in the roof. A gable vent at the garage might be the best bet and easiest

    3.) Complain to the home builder that the attic isn't vented properly
    - I bet this will get me no where

    4.) Complain that the a/c is undersized

    5.) Check with the neighbors and see if they are having the same problem

    Any feedback would be appreciated


  13. #26
    Join Date
    Jun 2005
    Location
    New York
    Posts
    205
    Post Likes
    How long has the system been on when you are taking these temps at the registers?

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums