  1. #1
    Join Date
    Feb 2004
    Posts
    360
    Post Likes
    We had a hot week a couple weeks back and at some point my mom noticed the a/c wasn't working very well anymore. She made the call for service on their 14 year old Bryant, they said they would come out the next week. Turns out it was a bad fan motor in the condenser. My dad replaced that himself to get it working again. Since they already had the appointment they decided to keep it, even though the system was working, and use it to get a check up.

    Here's the scary part. I asked my mom what the tech said about their system. She said they told her it was low on charge and they had to add freon. I asked my mom "where did it go"? These guys apparently convinced my parents that over time the freon leaks out through "pores" in the metal. I said b.s., if you're low on charge it went somewhere, you have a leak and the leak needs to be fixed.

    One more thing they said that scared me was that the system was "25% low on charge". They must have vacuumed the system down and weighed it right? I doubt it. You can't know how much volume a given system has and then derive a percentage can you? Aren't they all going to be different due to line set sizes and lengths? And if it was really 25% low on charge, wouldn't that have caused other problems like coil freeze ups, as well as possibly slugged the compressor?

    I couldn't convince my parents they recieved poor service. They think it is normal for charge to just disappear over time even though I told them it a system is done right it should never need freon to be added.

  2. #2
    Join Date
    Jun 2004
    Location
    Clayton,NC
    Posts
    407
    Post Likes
    Well since the system was cooling fine until the fan went and was fine again after it was fixed I dont think this was a blow and go. I think it was not low on freon and probably has no leak. This was a Bill and Go call.The owner probably feels they can make an easy 20-30 bucks per call by "topping" off the freon on those type of calls.

  3. #3
    Join Date
    Nov 2001
    Location
    Seattle, WA
    Posts
    8,352
    Post Likes
    You may be right or you may be wrong. Point is is your parents are happy. Why are you trying to make them unhappy?

    Communication is a funny thing. It is very possible that the tech attempted to explain to them in terms fitting to a non-tech person that systems do get or have pores in them that leak. Most old systems do. Most systems have little leaks around service valves, old and cracked joints, etc. The time spent trying to find a very small leak is too costly to the customer until that leak become bigger and tracable.

    Maybe the tech was wrong...but your parents are still happy and cool, I hope. I would not make a federal case out of this just to be right. But it does certainly give you reason to watch the system and overlook any further service if that would make you satisified.
    "The American Republic will endure until the day Congress discovers it can bribe the public with the public's own money.
    - Alexis de Toqueville, 1835

  4. #4
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes

    They may have recieved bad/poor service, BUT...

    ...there are several things you seem NOT to be familiar with.

    #1 Metal and braze joints do have pores. Whether they are large enough to cause problems is a different point.

    #2 Depending on the size of leak, it 'may or may not' be cost effective to fix and repair the leak. (although, I do prefer to find/repair them)

    #3 '25% low...' That can be an easy... What is the total system charge? Then if they weighed the amount (like they should have). They could easily figure out what percentage that is of the total charge. They would first have to make sure 'everything else' with the system is correct.

    #4 Line set lengths normally change the charge by oz NOT lbs.

    #5 'Low on charge causing problems...' Would all depend on conditions and run times.

    #6 'Low on charge cause slugging...' No possible way. Do you know what slugging means???

    #7 'I told them it a system is done right it should never need freon to be added...' I think this is the only thing you should assume to be correct in your post!
    (although a couple of oz in a system in 18-20 years can be achieved due to hose connecting/disconnecting)

  5. #5
    Join Date
    Feb 2004
    Posts
    360
    Post Likes
    Thread Starter
    That's why I posted, to see what you opinions are. So it doesn't seem to be a big deal. I just thought 25% seemed like a lot to lose and not hurt anything.

    I'm not an hvac person, just something I'm interested in learning about even though I never plan to actually work on any equipment. I always thought when you ran low on charge you risked a coil freeze up, then you would get liquid back to the compressor and that was called slugging since you can't compress a liquid.

  6. #6
    Join Date
    Nov 2001
    Location
    Seattle, WA
    Posts
    8,352
    Post Likes
    Maybe this will help you in your desire to understand all the possibilities.

    The condenser fan motor was bad which meant the head pressure went very high. Any leak of any size in the high side of the system would now become bigger as the increased pressure would drive out more refrigerant then would happen during normal head pressure with a properly operating condensor fan motor. Or the increased head pressure worked against the walls of the old and very thin copper and created a small leak.

    So when the tech got there he found that problem which would most likely not have been the main problem previous to the failed condensor fan motor hence no coil freezing or major loss of cooling previous to this event.

    Everything in these systems are dynamic. One failure can cause other problems in the system. When the head pressure went up the amp draw from the compressor increased which could now have set up a furture failure at the marginal contactor points or a failure at any loose wiring terminals anywhere within the system on the line voltage side.

    Or the compressor, old and loose, is now on the way out due to that extra load on the bearing, electrical winding, run capacitor, compressor terminals, etc, etc.

    So don't be surprised if a new problem arrives from this call which may show up in the next weeks or, especially, when the temperatures are the hottest and the system is under the heaviest load.
    "The American Republic will endure until the day Congress discovers it can bribe the public with the public's own money.
    - Alexis de Toqueville, 1835

  7. #7
    Join Date
    Feb 2004
    Posts
    360
    Post Likes
    Thread Starter
    That's very true, I didn't think of the head pressure magnifying any leaks that might have been there, or having even created new ones. At least now it makes sense to me, which is why I posted. Thanks!

    [Edited by dave and julie on 06-22-2005 at 03:45 PM]

  8. #8
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    Now go tell your parents that you learned something today and that the company servicing the equipment could have very well been on the up and up.

  9. #9
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Also, over time and especially after an adverse condition such as the condenser fan not operating, the system can simply change as to its function with the amount of refrigerant that is in it.

    There are many reasons for refrigerant to be low. Because weighing in of refrigerant requires that all components be perfectly matched, exact length of refrigerant lines be known and all mechanical components be operating within manufacturers specifications, I much prefer all systems be checked by superheat and subcooling.

    In other words, there could be exactly the proper amount of refrigerant in a system that the manufacturer originally required and the system charge could be off due to reasons not calculated by the manufacturer.
    Training is important!
    Practical Training is a must!

  10. #10
    Join Date
    Mar 2002
    Location
    Richmond, Virginia
    Posts
    4,264
    Post Likes
    Your parents 14 year old Bryant system has likely reached/or may very well be approaching it's normal life expectancy. Would you have felt better if they had coaxed your parents into spending several hundred dollars to repair a leak in this dinosaur? Sounds like they were looking out for your parents best interests to me.

    Doing this day in and day out increases a sharp technician's awareness on when to suggest investing in expensive repairs and when to take a wait and see attitude. The same rules don't always apply to each and every system. Glad to hear the system is back on line.
    There is nothing more frightful than ignorance in action....Mark Twain

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    No size of unit or line set info means we don't know how much charge it should have.(25% sounds alot, but not out of the ordinary).

    maybe it was 10% low and the tech stretched the truth(bad on him).

    Maybe it wasn't low at all(no way we can tell).

    Just check in with your parents once in awhile to make sure everything is ok.

    We all hope they weren't taken advantage of.

    Congrats on being children concerned about their parents welfare.


  12. #12
    Join Date
    Jul 2001
    Location
    Fairfield and NewHaven Counties in Commecticut
    Posts
    4,982
    Post Likes
    I have seen refrigerant blow out of schrader valves,when a condenser fan motoe goes bad.
    Quality and Value Service and Repair

  13. #13
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    My parents were a victim of a blow and go

    I was a victim of that 31 years ago and it's been costing me ever since.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  14. #14
    Join Date
    Apr 2005
    Location
    San Luis Obispo County, CA
    Posts
    215
    Post Likes
    Originally posted by mrbillpro
    My parents were a victim of a blow and go

    I was a victim of that 31 years ago and it's been costing me ever since.
    So was Monica.

  15. #15
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    Here's a link I was thinking about, when the idea of a 'small leak' happening over time was meantioned.

  16. #16
    Join Date
    Mar 2002
    Location
    Concord, CA
    Posts
    2,839
    Post Likes
    I think your suspicions are entirely reasonable Dave. The effect that low refrigerant has on performance is not linear. In other words, a charge that's low by 25% would most likely affect performance by more than 25%. If the system was that low it's highly unlikely that your dad would have been happy with its performance after he replaced the fan motor. And in the unlikely event that your dad was happy with its performance while it was that low then the “pores explanation” is a copout. The tech should have been looking for leaks or should have scheduled a time to come back and look for them.

    The odds that the tech was being technically precise as exemplified by jultzya or that he had Delta's desire to not confuse are pretty freakin low. It's much more likely that he's a typical hack padding the bill. The propensity of hacker AC guys to add a little Freon to pad the bill has been documented over and over again by investigative journalists. If so, the system is now overcharged. Its efficiency is down and so too will be its life expectancy. OR... It may be that the system was just a smidge low so he added a smidge but characterized it as more in order to charge more. In the one case your parents could lose a lot down the road. In the other they just got stiffed for a little up front

    In any event I'm more than willing to hang my so called peer out to dry simply because he either did the job wrong or he described his work wrong. A pro gets both right and can do so without confusing the customer. There’s simply no way around that conclusion.

  17. #17
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Irascible, well said.

    I'd bet good money if I went out to his parent's unit I'd find it overcharged. I'd go double or nothing the system probably uses a piston metering device.

    Overcharged piston regulated system.

    Sounds like double trouble to me.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  18. #18
    Join Date
    Mar 2002
    Location
    Concord, CA
    Posts
    2,839
    Post Likes
    Indeed. I'd bet good money and my own time. If he were local I'd go check it for free just to prove how right I am. Of course... if I were wrong you'd never hear about it.

  19. #19
    Join Date
    Feb 2004
    Posts
    360
    Post Likes
    Thread Starter
    I haven't asked them how the system is working since the tech's visit, I'll be sure to do that soon.

    I think it is a 4 ton in a 2750 sq ft. house with a finished walkout basement that adds another 1500 square feet. That thing has it's work cut out for it. Especially since it is a ranch house with the furnace at one end. The ductwork is nowhere near right, even with boosters in the ducts the furthest bedroom bakes in the summer and freezes in the winter. It's in a fairly affluent neighborhood too and recent construction. I've learned from you guys how critical installations are. When I was even younger and dumber than I am now, I just figured that was the best they could do. In reality the builder should have been made to fix the system.

    It's probably half my dad's fault, he wanted the condenser out of sight and where it is I bet it reciculates 25% of the air that goes through it. It's in the coner of a courtyard in front of the house.

    Anyway, I wish I could take you up on that bet, it would be interesting.

    Oh yeah, it's got an eletronic air cleaner too! I knew you would like to know that.

    I don't know if it is piston metered or not, I know mine is.

    [Edited by dave and julie on 06-27-2005 at 04:09 PM]

  20. #20
    Join Date
    Oct 2004
    Posts
    149
    Post Likes
    I got mine topped off a couple of weeks ago. It hadn't been serviced since it was installed in 1996. In a perfect world, it would not have leaked one bit, but I feel it was unrealistic for a unit to go that long without needing any (and it maybe needed one pound).

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •