4 ton carrier scroll compressor very very noisy, I had a owwned a scroll compressor but not that noisy . Unit does cool house down , suction return to compr. 55 degr.
-
06-22-2005, 01:41 PM #2
Pressure means nothing, make sure it's correctly charged and not slugging liquid and then put a sound -deadening blanket over it if it doesn't already have one.
If everything was always done "by the book"....the book would never change.
-
06-22-2005, 02:16 PM #3
Regular Guest
- Join Date
- Sep 2003
- Location
- Ford motor co.
- Posts
- 8
Thanks
It does not have a sound deading blanket . I will check for slugging liquid .
-
06-22-2005, 04:46 PM #4
Professional Member
- Join Date
- Dec 2004
- Posts
- 198
you can put a sound blanket around the sides of the scroll but do not cover it
-
06-22-2005, 05:22 PM #5
Regular Guest
- Join Date
- Jun 2005
- Posts
- 77
If its a Copeland Scroll then Copeland makes a custom blanket for it.
-
06-22-2005, 08:58 PM #6
Shoot it. I've never seen a blanket make even a slight difference in noise reduction.
The first thing I did to my YRA heat pump 10 yrs. ago was pull that heat trap off the scroll.There is nothing more frightful than ignorance in action....Mark Twain
-
06-23-2005, 07:56 AM #7
Sound blankets do reduce noise but if you have a nosiy compressor to start with they wont do much. They reduce the hum from the compressor. They are not a heat trap since the compressor is cooled by refrigerant not air. Airfow around a compressor has no effect on cooling, otherwise the compressors would have fins like the head of a motorcycle.
The real problem needs to be addressed which may be charge related, airflow related, oil return related, non condensibles or a damaged compressor. Most often the compressor is changed out of ignorance but the noise returns because the real problem was never resolved and by replacing the compressor inadvertantly the non-condensibles issue gets taken care of and the oil is now doubled in the system which allows the poorly run refrigerant lines which trap oil to now flow it.
-
06-23-2005, 09:02 PM #8
Self delete. Not worth my time.
There is nothing more frightful than ignorance in action....Mark Twain