    4 ton carrier scroll compressor very very noisy, I had a owwned a scroll compressor but not that noisy . Unit does cool house down , suction return to compr. 55 degr.

  2. #2
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,548
    Pressure means nothing, make sure it's correctly charged and not slugging liquid and then put a sound -deadening blanket over it if it doesn't already have one.
    If everything was always done "by the book"....the book would never change.

  3. #3
    Join Date
    Sep 2003
    Location
    Ford motor co.
    Posts
    8

    Smile Thanks

    It does not have a sound deading blanket . I will check for slugging liquid .

  4. #4
    Join Date
    Dec 2004
    Posts
    201
    you can put a sound blanket around the sides of the scroll but do not cover it

  5. #5
    Join Date
    Jun 2005
    Posts
    77
    If its a Copeland Scroll then Copeland makes a custom blanket for it.

  6. #6
    Join Date
    Mar 2002
    Location
    Richmond, Virginia
    Posts
    4,264
    Shoot it. I've never seen a blanket make even a slight difference in noise reduction.

    The first thing I did to my YRA heat pump 10 yrs. ago was pull that heat trap off the scroll.
    There is nothing more frightful than ignorance in action....Mark Twain

  7. #7
    Join Date
    Apr 2004
    Posts
    7,680
    Sound blankets do reduce noise but if you have a nosiy compressor to start with they wont do much. They reduce the hum from the compressor. They are not a heat trap since the compressor is cooled by refrigerant not air. Airfow around a compressor has no effect on cooling, otherwise the compressors would have fins like the head of a motorcycle.

    The real problem needs to be addressed which may be charge related, airflow related, oil return related, non condensibles or a damaged compressor. Most often the compressor is changed out of ignorance but the noise returns because the real problem was never resolved and by replacing the compressor inadvertantly the non-condensibles issue gets taken care of and the oil is now doubled in the system which allows the poorly run refrigerant lines which trap oil to now flow it.

  8. #8
    Join Date
    Mar 2002
    Location
    Richmond, Virginia
    Posts
    4,264
    Self delete. Not worth my time.
    There is nothing more frightful than ignorance in action....Mark Twain

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event