    What sizeTXV for Delfield Salad Prep Table(top rail).

    I have a Delfield (model #18699PTB, serial #BJT538601-T) R/I Cooler- Salad Prep table. Bottom cools just fine but the top does not refrigerate at all. LLS Coil energizes but still no refrigeration TD. Its hard working on this unit cause its the store's only prep table and they're always busy. So I set up a time and I want to have a LLS and TXV stocked when I get there.
    My question is this unit calls for a TXV part#351-6225 which I believe is low temp 0-*-40 degrees 1/4 ton. I have a 1/4 ton meduim temp 50-*-10 degree TXV. Does the top rail salad prep require a low temp TXV?

  2. #2
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    846
    Post Likes

    Lightbulb

    Need more info, ie..flavor refrigerant, pressures.... and if top rail has no fan then yes it is treated as low temp...

    Hope this helps...
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  3. #3
    Join Date
    Apr 2008
    Posts
    51
    Post Likes
    Thread Starter
    Thank you you've answered my question. It's 404a refrigerant and 220#/55#. It has no fans; just a cold rail on top. Its a salad prep table used to chill mayo, lettuce, tomato, veggies, etc. And should maintain a box temp of 35*-38*. Controlled by a low pressure switch cut-in @ 50* and cut out @ 25*.

  4. #4
    Join Date
    Oct 2003
    Location
    las vegas
    Posts
    1,505
    Post Likes
    size by the btu of compressor

  5. #5
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,719
    Post Likes
    Why make it hard? Call Delfield parts dept. and get a part number in minutes. You've got model and serial. In fact, OP already has part number. I googled it and saw in the Delfield online Parts Manual "Low Temp 1/4 ton TXV R-404a." Looks like a Sporlan.

    Since its not flowing at all, you might try swapping powerhead first... probably a KT43-SZ.

    Just my 2cents..

  6. #6
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    846
    Post Likes

    Lightbulb

    trippintl0 - you are spot on, and yes delfield uses spollan valves and thats all he would need to change providing solenoid is firing...
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  7. #7
    Join Date
    Dec 2008
    Location
    Nor•Cal
    Posts
    250
    Post Likes
    Every time I've called Delfield about TXV's, they are only able to give me the delfield part number; when I ask what sporlan number it is they tell me they don't know. Both the parts and the service departments tell me the same thing.

    Does anyone know of a cross ref for this?

  8. #8
    Join Date
    Apr 2008
    Posts
    51
    Post Likes
    Thread Starter
    Quote Originally Posted by mmmdave View Post
    Every time I've called Delfield about TXV's, they are only able to give me the delfield part number; when I ask what sporlan number it is they tell me they don't know. Both the parts and the service departments tell me the same thing.

    Does anyone know of a cross ref for this?
    Thats my problem. I can't get a part #351-6225 txv on a local purchase; recommended by delfield tech support. But their service manual for that model calls for a part #351-6273. These delfield part # mean nothing to the local suppliers as far as sizing a compatible valve.
    I did indeed call the manufacturer but the don't know the oem part #s. I looked in the service manual for the unit and it calls for a delfield part #3516273 (sporlan part #y1001-fbs- 1/4 -c) for the 2 evaps in r/i and for the top rail. Delfield told me the txv for top rail should be 0* to -40*.
    My problem is its the weekend so I have no technical support, no suppliers open, and have only til 5-8am tommorrow to complete the job. The only two Txv's I have is a sparlon #y1001-fbs- 1/4 -c and a sparlon #efs- 1/4 -c.

  9. #9
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    846
    Post Likes

    Lightbulb

    As far as crossing Heritage can help you with that....

    Both of those valves you have are med temp...

    And Ideas on what should be where and used, I'd like to think we do a pretty good job of helping on this site...
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  10. #10
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    846
    Post Likes

    Lightbulb

    Oh ya and dealing with various Tech supports , You just have to ask the right questions and you will get the answers you are looking for.

    IE.. If I were talking to Delfield tech support and he could not cross a part, I would simply ask him OK what is the upper or lower section rated for , They can answer that and even if they can't tell you what compressor, or valve goes in there they can tell you the required BTU's or temps needed to cool unit, and you should be able to take it from there.

    Sometimes it also the experience level of the support tecnician you are speaking to and you just have to ask question to his level or in a way he can understand them, they've got all the answers there as to the parts that go into treir equipment.

    And for those who need help diagnosing a problem keep in mind there are a lot of variables in the work we do and they are not there and can only go off the informatiom that we provide them with....so don't overthink things...

    I hope this Helps...
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  11. #11
    Join Date
    Jan 2008
    Location
    Lake Worth, FL
    Posts
    111
    Post Likes
    I've worked on those models before. The y1001-fbs- 1/4 -c is the correct one for both top and bottom. Are you sure it's not just low on refrigerant. When low it's the top rail that goes first. The lower evaporator coils have a tendancy to corrode and leak.

  12. #12
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    846
    Post Likes

    Lightbulb

    Unless the cold rail has fans in it then its to be treated as a low temp section...


    C - charge power head + 50*F - -10*F comercial temp / Medium temp
    Z - charge power head 0*F - -40*F low tem

    In order to bring the upper section down to temp and not be a the end of its range the proper choice would be the Z charge power head..


    Delfield specs these units to be at least +18*F 1 inch above cold well floor and to make it there in under 90 min. It would be a poor choice to choose the commercial power head.... But thats just my
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  13. #13
    Join Date
    Jun 2006
    Location
    n.texas
    Posts
    185
    Post Likes

    Rusty power head

    Change power head. Usally the problem. Under the insulation you will find it badly rusted. Also readly avalibale at supply counter.

  14. #14
    Join Date
    Apr 2008
    Posts
    51
    Post Likes
    Thread Starter
    To All:

    Thank you for your input. I changed the txv on the unit using a low temp power head on the new existing meduim temp txv replacement I had ready and it works like a champ.
    I tried changing the power head first and blowing nitro through the system. It had a lot of oil coming out of the txv body. When I put it back together it still had no flow. So I changed the entire body and it immediately started working.
    Thanks for all of your inputs.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •