Results 1 to 4 of 4
  1. #1
    Am I going crazy or is it true that you need a txv when using recip compressors? And start cap also.

  2. #2
    Join Date
    Apr 2005
    Location
    NE PA
    Posts
    697
    For the most part sounds like crazy.

    Only semi fact is that TXVs on a recip often require a hard start kit (start cap) due to the high head pressure at startup.

    paul

  3. #3
    Senior Tech Guest
    Yes.......your going crazy.

  4. #4
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    31,733
    High efficiency TXVs are usually non bleed so the system doesn't equalize during the off cycle. Scrolls usually start OK against it though many brands are starting to put hard start kits on them too. But on a recip, you may not start at all against a non bleed TXV without one.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •