Had a interesting call today. No cooling, found indoor unit with blown fuse on the curcuit board for the 24 volts, found that someone wired in a doorbell with the t-stat wires that went to the condencing unit and the doorbell went bad causing the fuse to blow. Customer was mad with me he thought I took to long tracing out the problem. Just wondering if anyone else has had this happen to them.