    What is the recommended method to add additional charge? Should the charge be sucked in or pumped in? The manual does not specify.
    Central Oregon
    Place the unit in a vacuum and pull it in.
    When the going gets weird, the weird turn pro. HST
    Memphis,TN
    If you do not know how to put the refrigerant in you should not try it .I say this hoping you do not suck the machine full of air trying to add some charge to it.The charging valve is located below the condenser it has a ball valve on it usually with a 5/8 male flare adapter on it.If the chiller is running or setting in a vacuum you can let the machine draw it in.
    Jan 2005
    http://www.isc.tv/pdf/msdsr123.pdf
    Check out the MSDS. You might want to be careful on how much you inhale( like all refrigerants ).
    North Florida/South Georgia
    Why do you think you need more refrigerant?
    All my leon freaked out!
    Aug 2000
    Austell, Ga.
    Yiiiiiiikes!!!!!!!
    This is getting "Scary"!!!!!
    Ain't "None" of us as smart as "All" of us..
    Central Oregon
    A simple question deserves a simple answer. Lets not read more into someones post than what is really there.
    maustin ........... very well said!
    thanks for the help!