    I have a Janitrol heat pump three zone system with a 5 ton and 2 3.5 ton units cooling 5500 sq ft. When may a/c is running it never shuts off. I just got a $843.00 electric bill for the month of May '05.
    Issue is: The thermostat is set at 78 degrees, once the temp reaches 78 degrees the units will not cycle off. Runs continously. Need Help.

    Could I have a stuck contactor? I did notice there were spider webs in the wiring area on the outdoors compressor unit?

    Current example: Downstairs 3.5 units reached the 78 degrees at 10:38 am as of now (10:58) still running. I can manually move up the temp to 79 and system shuts off.

    I have never had a electic billover $500. until this month.

    Orginally I had this problem with the units 3 threes ago. unfortunally the service guy that fixed it passed away. Several service people have looked at it and they say it is fixed then once a load is put on it, it happens again.


  2. #2
    Join Date
    Sep 2001
    Location
    Vancouver Canada
    Posts
    996
    Post Likes
    What kind of tstats are on these units. If you set the tstat to 79 will it cycle normally? Will it shutdown when temp reaches 79?
    "Go big or Go Home"

  3. #3
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    This is a duplicated post/thread. Please stick to one thread.
    Training is important!
    Practical Training is a must!

  4. #4
    Join Date
    Jun 2005
    Posts
    5
    Post Likes
    Thread Starter
    I have LuxPro Tstats. No it does not cycle off when it reaches 79.

    Example:

    Set at 79 once t-stats show 79 is will take from 29 to 25 minutes for the units to shut off. I have a degree swing set at 2.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •