    Hmm

    Worked on a Lennox two speed heat pump HP21. customer complained that it would run for an hour or two and then quit cooling. Gave a general once over, running at 70psi low side, under 200 high side, outdoor was 82 degrees F.

    After it ran for 60 min, the low side would gfadually drop to 0 psi and even into the HG zone a little. It never freezes up the indoor coil, not much freon flowing, low side not cold to reversing valve.

    From the txv equalizer bypass the line would freeze up down to the low side line and give the compressor some cooling, but not much, a little bit of cold r22 seemed to be flowing through the txv. I did the magnet trick on the receiver check valve that is in the outdoor unit right below the txv, turned it all off and ran the test on the TSC, a code 42 came up, which is a hot windings or ruined compressor sensors. Checked the sensor ohms, and running dc voltage on the TSC terminals for the Compressor sensor, all was well and I suspect it may have been an earlier recall code due to the low side pressure dropping, the volume drops too, as the low side line coming back to the reversing valve is not cold and returning any refrigerant. The high side never changes, not a bit, always holding below 200.

    Started it all back up, same problem, only sometimes it is a gradual decline in low side pressure, always to 0, sometimes it happens faster than usual, but back to 0. Tested reversing valve, temperatures are equal from return to compressor, very hot coming from compressor to reversing valve, as one would expect energized in cooling mode.

    I'm racking me brains on this one, do I have a back check valve in the outdoor unit or txv? When put in the heat mode, it all runs fine. I have several Lennox and heat pump books, but can't find the solution.

    Thanks, Mike

  2. #2
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    What is the subcooling in the cooling mode?

    Check the TXV in the indoor unit.

    [Edited by mark beiser on 06-19-2005 at 07:39 AM]

  3. #3
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Did you see it freeze the equalizer line at the indoor, or outdoor unit.

    If going to vacuum in cooling mode, trouble is usually at the indoor txv.

    Could be some filings got to it.

  4. #4
    Join Date
    Jun 2005
    Posts
    4
    Post Likes
    Thread Starter

    lennox hp21 heat pump

    The subcooling was around 18-20 degrees when it was working right, but that didn't happen for long.

    As the pressure progressively dropped to 0, the suction line would actually get warmer (from running at 50 F) to outdoor temperature, never hot like a leaking reversing valve.

    Thanks for the input, out of 11 techs no one wants to go near this one. Mike

  5. #5
    Join Date
    Jun 2005
    Posts
    4
    Post Likes
    Thread Starter

    lennox hp21 heat pump

    The freezing was at the txv equalizer tube in the outdoor unit, it goes down to the suction line a few inches from the compressor inlet.

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    I had acouple York Stealths do the same thing.

    They were always the indoor txvs.

    1 was bad.
    1 the equalizer line was brazed shut.
    1 had foreign garbage in it.


  7. #7
    Join Date
    Jul 2000
    Location
    Columbia, SC. USA
    Posts
    1,144
    Post Likes
    I would check the expansion valve indoor...it would seem your liquid line is restricted somewhere, causing the system to pumpdown...loss of suction pressure...there is probably a restriction entering the expansion valve causing your problem...alot of those lennox indoor expansion valves had flare fittings or compression fittings on the liquid line feeding them...Pump it down, and check for a piece of solder or slag or anything either restricting a screen or the valve itself..good-luck.

  8. #8
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes

    Re: lennox hp21 heat pump

    Originally posted by mkelley2
    Thanks for the input, out of 11 techs no one wants to go near this one. Mike
    Most people start blubbering when they hear "Lennox 2 speed", then if you say "Lennox 2 speed heat pump", they run screaming.

    I always enjoyed working on them. The HS/HP21 took all the fun out of it though, with the electronic module that saves diagnostic codes.
    The old HP11 units were a lot more interesting with all the tangled mass of controls and wiring, especially when I was like the 7th person from the 4th company to work on it in the last month.

  9. #9
    Join Date
    Jan 2004
    Location
    Midlothian, Virginia
    Posts
    195
    Post Likes
    could there be moisture in txv freezing it closed. i read at sporlan web sight pour warm water on em see if they work. if this works pump down install ll filter dryer
    Goodbyee stranger it's been nice. Hope you find your paradise! Hey it aint rocket science, "It's a Trade !"

  10. #10
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    love those hp21 units the old hp14 with all the relays and time delays were interesting to
    any way did you check the sensing bolb on the tax may be it is working properly or the tube is cracked and the valve isnt working.

  11. #11
    Join Date
    Jun 2005
    Posts
    4
    Post Likes
    Thread Starter

    lennox hp21 heat pump

    Thanks everybody. I guess I know what I get to do this week regarding the indoor txv. I was a little thrown by refrigerant being able to flow through the equalizer on the outside txv, turn the whole txv cold, but not raise the head up some.

    Thanks again, Mike

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •