    Does anybody have information on maintenance on these type of starters, 4160 volts Cutler Hammer. Across the line and autotransformer. As far as megging and doing maintenance. Also what type of instruments to use.

  2. #2
    Join Date
    Jun 2005
    Location
    ga
    Posts
    37
    the plant electricain certified on high voltage needs to rack out the starter and ground the stored energy in the motor.
    When you ask plant electrician to rack out the starter for service ask them to service the starter and meg the motor.
    4160 will reach out and grab ya most plants only want there electricians to service the starter

    [Edited by john f1 on 06-19-2005 at 09:20 AM]

  3. #3
    Join Date
    Aug 2000
    Location
    USA
    Posts
    4,990
    Its cheaper to pay a company that specializes in high voltage testing than to due it yourself. Its also safer. You dont use a meter to check for voltages they use a hot stick, you need special gloves, a special rubber mat, training and experience helps. Ive always found it interesting how you can "feel" the electricity as your hair stands up on your neck and arms when your working on a live 4160V circuit.
    Your poor planning does not constitute an emergency on my part!!!!

  4. #4
    Join Date
    Mar 2004
    Location
    North Carolina
    Posts
    400

    Hmm

    Freq drives are now available for 4160 who wants to service them ?
    is this really happening or not

  5. #5
    Join Date
    Jan 2005
    Posts
    62
    do not service for any reason.you must be a high voltage electrican.i know this because i am one.there is nothing in common with low voltage(anything below 600 vac is low voltage)anyone messing with that stuff that's not trained in it's service will get killed.it is that serious.just a friendly warning

  6. #6
    Join Date
    Dec 2003
    Posts
    1,739
    listen to what they say, 4160 is a different planet.
    there but for the grace of god, go all of us

  7. #7
    Join Date
    Jul 2003
    Location
    Texas
    Posts
    296
    Thanks, I agree with you all. Just checking. Unfortunatly thes machines are in Mexico and there is not a whole lot of trained people there. I will bring it to there attention.

  8. #8
    Join Date
    Jan 2004
    Posts
    1,176
    We service our own 4160 starters , we have approx 60 chillers with them.The only thing we don't do is hi pot test them as the company doesn't want to invest 8k in equipment so we sub that part out.

  9. #9
    Join Date
    Jan 2005
    Posts
    32
    That's the problem with being out of the good ol' U.S.of A. Complain as we might OSHA keeps us safe at times.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event