Results 1 to 13 of 15
    Oct 2001
    why low pressure gauge on R-11 chiller would
    go from 14"Hg to O and back to 14" in about 10 seconds?
    After seeing it twice I decided to find out what was going on.
    It didn't take to long to get the answer.
    I will give you only one clue:
    Nothing noticeable different was happening in operation of the chiller during this event. No change in sound of the motor and no change in amp draw.
    May 2005
    Calgary, Alberta, Canada
    Was the building operator playing with some valves??
    Yes we have air conditioning in our igloos.
    Oct 2001
    No. Water flow was always the same.
    Jan 2001
    So.Cal
    oil slugging
    Oct 2001
    No oil slug.
    Jan 2005
    What was the chilled water temp at the time?
    Oct 2001
    I think that chilled water was somewhere around 44 deg.
    Feb 2005
    Dothan, Al
    What was the delta 't' ??
    Oct 2001
    10 degrees.
    Jan 2005
    What type of chiller?
    Oil differential pressure guage/switch leaking through?
    Trapped liquid in gauge line?
    somebody stepping on your hose as they marched by your work site?
    Oct 2001
    LOL
    Evaporator gauge is installed on the control panel along with condenser and oil pressure gauges.
    R718 is right. These changes in evaporator gauge reading were caused by momentarily presence of liquid refrigerant in a gauge line.
    The question is; how this liquid was getting in there?
    Jan 2005
    Sigma,
    Does this occur constantly while chiller is running, or just after start up and eventually quits?