Results 14 to 22 of 22
Thread: Is the compressor dead?
-
06-25-2005, 02:23 PM #14
Regular Guest
- Join Date
- Jun 2005
- Posts
- 5
Ok. I have replaced it. There was about 56oz r22 instead of 73oz according to the label on the condenser. When I checked for leaks I found one on the pipe entering the condenser and probably that was the problem with the unit and my old compressor is not bad. Anyway I did not put it back.
-
06-25-2005, 03:24 PM #15
so it was low on freon and running high suction low head pressures??? Hummmmmmmmmmmmm.
If everything was always done "by the book"....the book would never change.
-
06-25-2005, 03:46 PM #16
so what was the real problem with the unit. subcool auperheat presures and line temps and td. if the old compressor is still good did you charge for the new one or just the repair
-
06-25-2005, 08:21 PM #17
Professional Member
- Join Date
- Dec 2002
- Posts
- 9,871
hvac r us 2 agree on a lot of things
Originally posted by hvac r us 2
The question I always ask my guys is "why did it die?"
Make no mistake a 7 year old compressor just didnt die, it was murdered!
Dont let anybody kid you, there is a reason that compressor failed and it's not becuase it was defective, old age, a lemon, hit by lightning, voltage spiking...
You know all the popular answers techs give when they really dont know.
Without knowing why the first compressor failed, stands to reason the second compressor will also have the same fate.
Ask yourself,
How much oil is left in the old compressor?
Is the unit mis applied?
Long line not done correctly?This is one. Poor filter maintenance could be the culprit.
Low ambient not done right?
Wrong metering device?
Bad airflow?
How much refrigerant did you take out, was it overcharged?
You get the idea...the answer is out there!
-
06-25-2005, 08:53 PM #18
Professional Member
- Join Date
- Sep 2002
- Posts
- 506
smokin68
Professional Member
Registered: Jun 2003
Posts: 1332
so it was low on freon and running high suction low head pressures??? Hummmmmmmmmmmmm.
__________________
Is it really any easier doing it twice?????
Hmmmmmmmmmmm is right......doesn't sound like a low charge would give you the pressure reading that you posted.
I think there is something else to this,don't you?
-
06-25-2005, 09:27 PM #19
Regular Guest
- Join Date
- Jul 2000
- Location
- Columbia, SC. USA
- Posts
- 1,143
I'm So CONFUSED!!!!!!!!!!!!!!!!!!!!!
-
06-25-2005, 10:39 PM #20
mistake or not one thing i can say once you burn out a compressor it is history and you eat the mistake. putting it back it wont be runnig for long if at all and you just waisted two compressors
-
06-25-2005, 11:05 PM #21
Green oil....Hmmmm
Copper Sulfate? Has a nice odor too....
-
06-25-2005, 11:24 PM #22
Regular Guest
- Join Date
- Dec 2003
- Posts
- 154
TXV gaged open?