using a hygrometer from radio shack, i'm getting a reading of 44%RH in the house. i placed the hygrometer on a supply vent while the a/c was running and it went to 64%, then the minute the compressor stopped running and the airhandlier ran for a couple of minutes the RH went to 80%. thermostat set at 73deg. and the supply air at 52deg. is this normal?
-
06-17-2005, 02:29 PM #2
more or less, yeah.
The relative humidity of the air coming off the cooling coil will be pretty high, particularly right after the compressor shuts off.
-
06-17-2005, 05:42 PM #3
Regular Guest
- Join Date
- Jan 2005
- Posts
- 22
That's why it's called "relative" humidity because it is "relative" to the temperature. Since colder air holds less moisture, you will get a higher RH reading on the supply air compared to the room temp air.
-
06-17-2005, 07:29 PM #4
Adding to what takeflight said
Get a two measuring bowls
One that holds one quart the other holds two quarts.
Fill the small bowl to the top.
That bowl represents 'cold' air.
And is now at 100% relative humidity.
When you heat air up, it expands so to speak.
(pour that water into the two quart bowl)
The bigger bowl now represents warmer air.
And as you can see, the bowl is half full OR
50% Relative Humidity.
We didnt' change the amount of moisture, we just changed the temperature of the air.
-
06-17-2005, 07:44 PM #5
You forgot one little detail wormy.
Now you got 2 dirty bowls
-
06-18-2005, 05:05 AM #6
Professional Member
- Join Date
- Feb 2003
- Location
- Huntsville,AL
- Posts
- 4,125
put gauge in baggie with salt+ h2o -- after few hours, should read 75%RH -- just to check gauge
-
06-18-2005, 07:25 AM #7If you're running 44% RH in your house as a whole, you're doing great if you live in a humid climate.Originally posted by aj1213
using a hygrometer from radio shack, i'm getting a reading of 44%RH in the house. i placed the hygrometer on a supply vent while the a/c was running and it went to 64%, then the minute the compressor stopped running and the airhandlier ran for a couple of minutes the RH went to 80%. thermostat set at 73deg. and the supply air at 52deg. is this normal?
BTW, when supply air is right at the discharge side of the cooling coil, it is at 100% relative humidity. That is because the cooling coil itself is at or below the dew point of the return air passing over the coil. So, if 44% RH return air at a given dry bulb temp is passing over a coil containing refrigerant boiling at, say, 45 degrees Farenheit, the moisture in the return air will condense on the cold coil's surface. This same air, now called supply air, leaves the coil at 100% relative humidity.
Relative humidity is defined as the amount of humidity in the air at a given temperature vs. the same air at the same temperature but with all water vapor at 100% saturation. Or, the ratio of the amount of water vapor in the air at a specific temperature to the maximum amount that the air could hold at that temperature, stated as a percentage.
This is where psychometrics and psychometric charts come into play...a very interesting field all in itself."In this house we obey the laws of thermodynamics!"
- Homer Simpson
-
06-18-2005, 12:04 PM #8
Professional Member
- Join Date
- Sep 2002
- Location
- South Dakota
- Posts
- 6,579
I don't have the time to write custom answers to many of these types of questions so instead I will post an article that covers the question in the article if you take the time to look for it.
Besides, the rest of the information is also useful.
http://hvac-talk.com/vbb/showthread.php?threadid=33469
-
06-19-2005, 01:43 AM #9
NormChris,
It said...
The following article was taken from a larger work on psychrometrics by Norm Christopherson
were's the rest of it
I really need a refresher in psychometrics.
-
06-19-2005, 01:56 AM #10
Professional Member
- Join Date
- Sep 2002
- Location
- South Dakota
- Posts
- 6,579
Originally posted by wormy
NormChris,
It said...
The following article was taken from a larger work on psychrometrics by Norm Christopherson
were's the rest of it
I really need a refresher in psychometrics.
I wrote the book which I titled "Applied Psychrometric & Airflow for HVAC Technicians" when I was teaching HVAC fulltime at a California community college.
At that time I self-published the book for use as the text for a semester long class I was teaching.
Now that I am a factory training specialist for York International York has decided to publish the book and sell it through the network of York, Coleman and Luxaire distributors.
The book is currently being revised by a graphics illustrator to make the examples look more professional. As soon as it is ready I will be using the book as the text for a two-day York seminar available through York, Coleman and Luxaire distributors. Or, you will be able to purchase the book alone.
I highly recommend you attend the two-day class as the personal instruction I provide makes understanding this important and practical subject easy to follow.
If you want a class in your area contact your local distributor of York, Coleman or Luxaire products and ask them to schedule a class for this fall.
Norm
-
06-19-2005, 06:06 AM #11
Regular Guest
- Join Date
- Sep 2004
- Location
- Vancouver, Canada
- Posts
- 30
Off topic, but here is a little tip for calibrating hygrometers using a bit of salt and a plastic bag.
http://www.cheaphumidors.com/Merchan...owto_calibrate