i have today unit no matter how much r22 i put on it liquid line have same temp. and evapor. coil freezin up
You gotta be kidding.
This is a joke,right?
I'm sorry but a professional member does not ask this type of question.
Are you a student?
If so where?
We've been doing so much,for so long,with so little, that now we can do almost anything, with nothing at all.
Gotta agree with a/c Don. You come across sounding like a moron. Either provide a few more details or don't bother posting such dumb thing.
"Go big or Go Home"
cachorro; got another compressor handy ???!!!
Da Threadkilla
HA HA IM BUSTING MY GUT LAUGHING.
STOP PUTTING IT IN! 3 TANKS SHOULD BE ENOUGH!
HOW MANY TIMES HAS THE GUAGE GONE AROUND?
HOW MUCH DO YOU CHARGE FOR A SERVICE CALL?
Long moment of silence.
Maybe you should have checked to see if the txv is working.
Maybe you should ride with another tech for awhile.
Maybe you should take courses for trouble shooting.
Got to the "FOR YOUR INTEREST" area, and READ for the rest of the weekend!
Then come back and ask questions.
What did he say?
I think he said, I dumped a $hit load of 22 in a system today and the darn coil kept freezing after i emptied a whole jug into it.Originally posted by hiltontech
What did he say?
Of course I apologize if it was a 100 horse unit, and he was using 30 lb. cyclinders to charge it.
That's what I thought he said, I wonder what the compressor has to say about that..
HiltonTech
Actually, that's not what he said.........He said he put the r22 "on it"....maybe that's why its not changing the line temp and it's still freezing up! I always thought you had to put the freon in it.
you guys may think this is funny but ill tell you there are
probably 98% of all residential techs that do not know how to charge txv systems. or for that matter orfices. most think they just got to get a 60 or 70 lb suction and thats it. they donot understand subcooling and superheat which if you dont you do not understand the refrigerant process.
i find systems overcharged all the time. they think when a compressor fails it just failed and theres really not a reason. just install a new one and go on.
I agree with airworx, too many techs who just flat out do not know. I once got into an argument with a tech who had been doing res/commercial work for 30 years about the existence of SH and SC.
Cachorro,
Just a few questions:
1.) What were your system pressures before adding refrigerant?
2.) Did you take Superheat and Subcooling measurements?
3.) No airflow restriction?(plugged filter, dirty evaporator coil, blower motor running at correct speed)
4.) What made you think the system was low on charge?
5.) What were the ambient temperatures and indoor wetbulb temperatures?
6.) Last but not least, HOW MUCH REFRIGERANT DID YOU ADD?
Please clear up these questions and possibly get us the make/model numbers of the equipment you are working on so we can TRY to help.
As always with respect,
websy
[Edited by websy on 06-18-2005 at 11:01 AM]
Yes we have air conditioning in our igloos.
Originally posted by airworx
you guys may think this is funny
I wasn't laughing.
This happens all too often all over the place. And its because of poor training received by the unknowing, while being led, or thrown to the wolves by uncaring bosses, and or owners.
did amrik go into the feild and register under a new name?Originally posted by cachorro
i have today unit no matter how much r22 i put on it liquid line have same temp. and evapor. coil freezin up
Okey guys i fixe today the ploblem and, was the txvs stock close, I put about 1 1/2 lb of r22and i did subcooling the txs wasn't opening and starb the evapora coil and it whay was freezzig I replace txs and unit runing 100%
airworx those 98% keep our jobs goin at the expense of the customer but you are right it is every where
hey hey guys I got this under the ploblem was the txs stock close estarbeen mi evapor.coil I put 1 1/2 lb of r22 and the temp. din't change on my subcooling liquid line and i teke my reeding an wet bulb and dry bulb and din't match whit temp out of vent. I replace txv and unit ran 100%