    Should the outside or inside of a house be used to figure load calc.

    1 contractor measured inside (sd 2.5 ton a/c)
    the other measured outside & sd (3 ton a/c)


    Thanks

  2. #2
    Join Date
    Jan 2005
    Posts
    340
    Post Likes
    Originally posted by lit'l cat
    Should the outside or inside of a house be used to figure load calc.
    To do it professionally requires a room by room calculation. You can't do that from outside. Sounds like the 'outside' guy is just calculating the square footage of the house - and that won't yield reliable results.

  3. #3
    Join Date
    May 2004
    Posts
    8,623
    Post Likes

    Hmm

    A whole house load calculation CANNOT be performed accurately by measuring square footage for the outside of a house.

    The type of construction entails both inside and outside factors as well as design temps for your area.
    I usually do a room by room load instead of a whole house load so that I can be sure of getting the proper amount of air to each room.

    Hope this helps.

  4. #4
    Join Date
    Apr 2005
    Location
    Richmond, Virginia
    Posts
    365
    Post Likes
    The difference may be in "block load" and "sum of peaks load". I'm not familiar with manual J, I use the Trane 700 load program.

    The block load is just that-the length and height of the walls are mesured (can be done on the outside of the house) along with the area of glass. Taking into account the orientation of the walls (N, E, W, S) and the load is run.

    Sum of peaks is a room by room calculation.

    The sum of peaks load will be higher than the block load since the peak load of each room is added together. This is used to calculate how much air needs to be delived to the room.

    The block load is used to select equipment.

    Both loads should be performed to select equipment and determine the airflow for each room.
    Sean Cantrell

  5. #5
    Join Date
    Jan 2005
    Posts
    340
    Post Likes
    Originally posted by sean88
    The block load is just that-the length and height of the walls are mesured (can be done on the outside of the house) along with the area of glass. Taking into account the orientation of the walls (N, E, W, S) and the load is run.
    Interesting. So a 2500 square foot home with eight foot ceilings shows the same load as a 2500 square foot home with 11 foot ceilings?

  6. #6
    Join Date
    Apr 2005
    Location
    Richmond, Virginia
    Posts
    365
    Post Likes
    Yes it would if you had a 3 ft plenum dropping the ceiling height from 11 ft to 8 ft. All wall mesurements should be floor to floor with the plenum taken into consideration.

    It would not if you were lowering the total building height 3 ft.

    I came from a commercial background so like I said I don't know what Manual J states how loads should be run. I use Carrier or Trane programs.
    Sean Cantrell

  7. #7
    Join Date
    Jan 2005
    Posts
    340
    Post Likes
    Sorry, I overlooked that you said "height and length" of the outside walls. I must have read that as "width and length". You must have meant "height, width, and length".

  8. #8
    Join Date
    Nov 2002
    Posts
    94
    Post Likes
    Thread Starter
    I guess the 1st Guy (outside measurements)did a block load. He sat down & calculated everything in front of me. Oddly he did say I should add 2 supply ducts on either end of the house to make enough airflow. (brick rancher 1954 currently 7 rtns on outside walls & 11 supply ducts on inside walls but 2 are sm ducts in the bathrooms)

    Other contractor (2.5ton ac) sd my current furnace possible was so oversized to make sure enough airflow. But he didnt think I needed any additional supplies w/a 2.5 Ton a/c

    (as if I wasnt already confused enough)

  9. #9
    Join Date
    Apr 2005
    Location
    Richmond, Virginia
    Posts
    365
    Post Likes
    If you have a sketch in pdf format with dimensions of walls and windows. I can run a load for you in 20 min.

    I also need to know what the walls are made of brick, insulation, gypboard, is there is any insulation in the roof and what kind of windows do you have--single pane or double pane.

    e-mail is seancantrell@comcast.net
    Sean Cantrell

  10. #10
    Join Date
    Jan 2005
    Posts
    340
    Post Likes
    Originally posted by sean88
    If you have a sketch in pdf format with dimensions of walls and windows. I can run a load for you in 20 min.
    Don't you also need to know where the OP lives, what design temperatures he desires, and the orientation of the various windows and doors? How about the number of fireplaces and the number of people living in the house?

  11. #11
    Join Date
    Feb 2005
    Location
    MA
    Posts
    150
    Post Likes
    Don't forget infiltration - that 51 year old house may leak like a sieve!

  12. #12
    Join Date
    Nov 2002
    Posts
    94
    Post Likes
    Thread Starter
    PS you are right about this house being leaky but oddly 2 1/2 years ago we got bids to replace AC only, one contractor mentioned in a few years we wd have to replace furnace so why not wait & replace both. Sounded good BUT since then weve replaced single pane windows which were VERY drafty (all needed to be reglazed) with double pane low E gas windows & the 2 new bids we have received are the same as 2 years ago (back then 1 sd 2.5 ton & 2 sd 3 ton)

    Anyway, I'm not sure how much difference it makes but I would think it would count for something

  13. #13
    Join Date
    Jan 2005
    Posts
    340
    Post Likes
    Originally posted by lit'l cat
    I'm not sure how much difference it makes but I would think it would count for something
    When you get a room-by-room Manual J done, you'll know.

  14. #14
    Join Date
    Apr 2005
    Location
    Richmond, Virginia
    Posts
    365
    Post Likes

    Post

    Don't you also need to know where the OP lives, what design temperatures he desires, and the orientation of the various windows and doors? How about the number of fireplaces and the number of people living in the house?

    In central VA - richmond - tidewater area design is 95 F 76 wb.

    Fireplaces are negliable since they would not be used for heating purposes. They do contribute to infiltration due to stack effect if the damper is not closed.

    For a family of 4 thats 450x4=1800 mbh total or .15 tons.

    Hopefully the sketch would have a north arrow, but you're right need the orientation of walls too.
    Sean Cantrell

  15. #15
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes

    Cooling Load

    Originally posted by lit'l cat
    Should the outside or inside of a house be used to figure load calc. 1 contractor measured inside (sd 2.5 ton a/c) the other measured outside & sd (3 ton a/c)
    1,800 Sq.Ft., 300 Sq.Ft total Window area with Low E,
    _____ Use 2.5 Ton ____

    Low E ( S.H.G.C. ~ 0.46) requires 0.5+ ton less than CLEAR Glass ( SHGC 0.75). Room Temperature desired 75'F

    S.H.G.C. Solar Heat Gain Coefficient
    S.H.G.C. = 7/8 * Shading Coefficient

    100 Sq.Ft. difference in floor + ceiling area may make Cooling load difference of << 0.2 ton
    I use close to the Inside Area.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  16. #16
    Join Date
    Nov 2002
    Posts
    94
    Post Likes
    Thread Starter

    Re: Cooling Load

    Designer Dan,

    Your post sd 1800sq ft use 2.5 Ton. My house is ~ 1600sq ft. In theory, that would make the tonnage even less, then wouldnt I have an airflow problem?

    Before you answer, this is more a general question since I realize you have no detailed info abour my house

  17. #17
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes

    Exclamation Cooling Load Variations

    Originally posted by lit'l cat
    Your post sd 1800sq ft use 2.5 Ton. My house is ~ 1600sq ft. In theory, that would make the tonnage even less, then wouldnt I have an airflow problem?
    It ALL Depends on ...

    Blower + Blower Settings + Condenser +
    + Duct + Duct Transitions + Outlets + dT + %RH
    + Time of Day + Day + Month + ... +

    + Sunny + Cloudy + use of Ceiling Fans +
    whether you have several visitors +

    + How it ALL Works together AS A SYSTEM! ? ______
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  18. #18
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes

    Re: Re: Cooling Load

    Originally posted by lit'l cat
    Designer Dan,

    Your post sd 1800sq ft use 2.5 Ton. My house is ~ 1600sq ft. In theory, that would make the tonnage even less, then wouldnt I have an airflow problem?

    Before you answer, this is more a general question since I realize you have no detailed info abour my house

    Less tonnage on existings ducts is seldome a problem.The throw from the supply grilles will be less ,with less total cfms,unlikely enough less to be a problem.Todays top of the line two speeds,run on low most of the time,and there's no problem.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •