There are many issues to talk about in this thread…
I am guessing pressure testing with Nitrogen and utilizing a good micron gauge is out of the question?
I doubt very seriously you are hearing air gurgling. What you are hearing is the fact that the liquid line is not a full column of liquid refrigerant.
This is probably due to air that is being trapped in the condenser/moisture freezing at the metering device. Easy to tell, fluctuating pressures, high head, high sub-cooling...
Typically head is high because you are reading more than one compound, instead of reading just the refrigerant pressure you are reading refrigerant + air + moisture…it’s a false reading.
This in turns jacks up your sub cooling number to some ridiculous levels, like 30/40 degree’s.
Although I am assuming this is a side job you still should be practicing proper refrigeration techniques.
Get rid of the refrigerant, add liquid line dryer, pressure test with Nitrogen, evacuate with a Micron gauge, confirm airflow, set charge accordingly (by superheat with a piston, by sub cooling with TXV)
Slow down, do it right and stop doing side work…especially for family!