Thread: Drain line help!
-
06-14-2005, 11:52 PM #1
Regular Guest
- Join Date
- Jun 2005
- Posts
- 12
Drain Line Issue - Updated w/ PICS
The setup:
Air-handler in attic
Drain line leaking somewhere in between 2nd and 1st floor.
My thought:
Run new drain line.
The problem: I ran 20 ft of 3/4 PVC to the opposite end of the attic because it had easy access to drill in to the wall and add a drain outlet. The PVC is at an angle and the drain outlet is 8-12 inches below the handler line.
After the first day there was water in the opening after the p-trap and if I went to the outside drain and did a quick syphon the water flowed out.
Since the water was coming out the presumable breathing hole I added a temp plug but is this the best thing to do or should I do something different?
Help please......
-
06-15-2005, 12:31 PM #2
Regular Guest
- Join Date
- Jun 2005
- Posts
- 12
Update - Photo 1
Here is what I have. The line from the unit does not look like a regular p-trap. This morning I removed the trap cleaner plug and a bunch of water flowed out. It also appeared that water leaked around the plug overnight and cause some water rings on the ceiling drywall.

[Edited by gman69_1999 on 06-15-2005 at 03:00 PM]
-
06-15-2005, 12:32 PM #3
Regular Guest
- Join Date
- Jun 2005
- Posts
- 12
Update - Photo 2
Here is another view:

[Edited by gman69_1999 on 06-15-2005 at 03:01 PM]
-
06-15-2005, 12:34 PM #4
Regular Guest
- Join Date
- Jun 2005
- Posts
- 12
Update - Photo 3
And here you can see the main drain line crossing the overflow pan line. Notice it (main drain line) is on a decent drain angle.

[Edited by gman69_1999 on 06-15-2005 at 03:01 PM]
-
06-15-2005, 12:35 PM #5
Regular Guest
- Join Date
- Jun 2005
- Posts
- 12
Update - Photo 4
And here is the outside view of where it drains:

[Edited by gman69_1999 on 06-15-2005 at 03:02 PM]
-
06-15-2005, 12:38 PM #6
Regular Guest
- Join Date
- Jun 2005
- Posts
- 12
What I did today
So this morning I went ahead an put a bead of silicon around the trap cleaner plug as I suspect that the water is leaking from there. What I am more concerned about is the fact that the water is at that plug point as it was not prior to me running the new line.
If it doesn't leak in the next 24 hours, I will feel better but not knowing what is happening with the water in the PVC will be on my mind all the time.
Any ideas or suggestions?
-
06-15-2005, 12:51 PM #7
Post some pics that work...
How tall are you Private???!!!!
-
06-15-2005, 12:54 PM #8
Regular Guest
- Join Date
- Jun 2005
- Posts
- 12
??? - Pic's are displaying here
I can see the pics just fine??..??I went ahead and moved the images to a different domain to see if that helps.
[Edited by gman69_1999 on 06-15-2005 at 03:02 PM]
-
06-15-2005, 03:03 PM #9
Regular Guest
- Join Date
- Jun 2005
- Posts
- 12
Should work now
Images should be ok now
-
06-15-2005, 03:36 PM #10
Professional Member
- Join Date
- Jul 2001
- Posts
- 3,112
You installed the trap backwards.
-
06-15-2005, 03:39 PM #11
Professional Member
- Join Date
- Jul 2001
- Posts
- 3,112
Sorry.I didn't look at the picture correctly. My mistake. How did the trap get scorched and distorted? Is the trap restricted? Could be it can't drain fast enough because of the distortion.
-
06-15-2005, 04:06 PM #12
Regular Guest
- Join Date
- Jun 2005
- Posts
- 12
That is what the AC service company did 2 years ago when they put the new unit in. It looks like they made their own trap.
Beyond this, prior to me running the new PVC line, the trap cleaner (or open top of the T) did not have water setting in the opening or spilling out for that matter. Is it possible with the length of the new run that I need a real trap all together or can I do without?
-
06-15-2005, 04:51 PM #13
Regular Guest
- Join Date
- Nov 2004
- Location
- Atlanta, Ga. burbs
- Posts
- 281
This is your answer to your question
I had a problem with my drain line. Installer flat out did it wrong and I could not get him back out. Someone here pointed me this site at Trane.
http://www.trane.com/commercial/issues/iaq/iaq5.asp
I agree the line looks constricted. Maybe they tried to make the trap by heating the plastic pipe. You can make one from elbows very easily. See the link and good luck.


Reply With Quote