    wentout on a call today customer had ac on todays staite said was not cooling, I took cover off condenser suctionline had 2 inches of ice around it.
    compressor had ice all around it.
    went in crawl there was all water dripping off the suction line insulation evap was a block of ice.
    things only 5 years old dam.
    finally got my gauges on it gave it a liquid charge not running of course sucked up 3 pounds of refrigerant.
    told customer not to run it for a day let all the ice melt in the evap then i will check it again to cap off my charge see what wrong with the thing.

  2. #2
    Join Date
    Jun 2001
    Posts
    3,916
    Post Likes
    Originally posted by TheDuke
    wentout on a call today customer had ac on todays staite said was not cooling, I took cover off condenser suctionline had 2 inches of ice around it.
    compressor had ice all around it.
    went in crawl there was all water dripping off the suction line insulation evap was a block of ice.
    things only 5 years old dam.
    finally got my gauges on it gave it a liquid charge not running of course sucked up 3 pounds of refrigerant.
    told customer not to run it for a day let all the ice melt in the evap then i will check it again to cap off my charge see what wrong with the thing.
    Your kidding right ? How can you charge a frozen unit properly ?

  3. #3
    Join Date
    Mar 2002
    Location
    Richmond, Virginia
    Posts
    4,262
    Post Likes
    I'll be back. This one is going to be too hard on my brain right now.
    There is nothing more frightful than ignorance in action....Mark Twain

  4. #4
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,850
    Post Likes
    oh boy, lincoln tech must be proud of you!!!!!!!!

  5. #5
    Join Date
    Mar 2005
    Posts
    18
    Post Likes
    is this a joke???

  6. #6
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,794
    Post Likes
    Mr. Duke, I highly recommend you spend some time studying the effect of airflow over an evaporator coil.

    Did you even bother to look at the filter and blower wheel? Tell tale signs of what that coil underneath all that ice might look like.
    Building Physics Rule #1: Hot flows to cold.


    Building Physics Rule #2:
    Higher air pressure moves toward lower air pressure


    Building Physics Rule #3:
    Higher moisture concentration moves toward lower moisture concentration.

  7. #7
    Join Date
    Aug 2002
    Posts
    490
    Post Likes
    Thread Starter
    ok why is every one picking on me!
    did like 7 calls today just came home little while ago
    stuck in traffic half the day tryin to make a livin here.
    yes first thing i did was check the filters then i checked the evap seen the ice then looked up at the suction line seen all the water dripping then i told homeowner to turn it off went out to the condenser remover cover seen all the ice out there.
    told homeowner to run the blower to melt ice checked to see water pooring out of evap drain line
    chipped away at ice gave it about 30 to 40 minutes then plugged into the system took standing pressure gave it a checked it out and gave it a charge like i said above.
    told homeowner not to run it for the nite tomorrow i will go and see what i can find.
    yes im here cause im looking for some advise of corse from other techs

  8. #8
    Join Date
    Mar 2002
    Location
    Richmond, Virginia
    Posts
    4,262
    Post Likes
    What other kinds of things did you find on the other 7 calls? Just wondering what kind of problems you're experiencing in your neck of the woods.
    There is nothing more frightful than ignorance in action....Mark Twain

  9. #9
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    addvise on iced up unit
    shut it down leave the blower run. go back at the end of the day or the next day and find out why it iced up.
    never add refrigerant to a unit that is iced up

    did 15 calls today and got in at 9.30
    it is part of the trade and happens every year

  10. #10
    Join Date
    Jun 2001
    Location
    San Diego, CA
    Posts
    1,185
    Post Likes
    15 calls? Geez you got a helicopter or something?

  11. #11
    Join Date
    Feb 2002
    Location
    Yuma, Arizona
    Posts
    943
    Post Likes
    Originally posted by tinknocker service tech
    addvise on iced up unit
    shut it down leave the blower run. go back at the end of the day or the next day and find out why it iced up.
    never add refrigerant to a unit that is iced up
    The last line here is the most important!!!!
    More techs have killed compressors by Just adding a few pounds!Unless the coils are clean, blowers/fans working properly and the ducts are clear (and you checked each) Don't add a few pounds!!!
    And as for long days, out here it's been over 100° for over a month and that goes with the territory.

    We are also not trying to just bust your chops but to keep you on the proper road and not make to many mistakes.

    By the way it's 10PM and still 84°f out side.
    (Another cool day in Paradise!)

    Yuma,
    What is snow? Is it that white stuff in a freezer?

  12. #12
    Join Date
    Nov 2004
    Posts
    98
    Post Likes
    did you use the yellow jacket ice pick, or the robinair model?

  13. #13
    Join Date
    May 2005
    Location
    Seabeck, WA
    Posts
    1,870
    Post Likes
    I love this site. Plumbers respond to HVAC calls. . . .
    Live for yourself and ask no one to live for you.

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.