Results 1 to 7 of 7
-
06-13-2005, 10:07 PM #1
Regular Guest
- Join Date
- Jun 2005
- Posts
- 1
I have a 13 yr old Rheem system that has failed. It is an electric heat pump outside unit model is RPGC-042JAS. What ton size is it and a contractor wanted to replace it with a 3 ton Bryant Evolution series with puron. Should it be a 3 or 4 ton. He said Bryant doesn't come in half tons. Please help with info.The old system worked fine in the summer and a little cool in the winter months.Hard time keeping up on cold windy days.SHOULD HE BEING GOING DOWN TO A 3 TON UNIT?
[Edited by john3an3 on 06-13-2005 at 10:24 PM]
-
06-13-2005, 10:10 PM #2
Professional Member
- Join Date
- Sep 2004
- Posts
- 172
looks like 3 1/2 ton, how is your new contractor coming with his load calculation?
-
06-13-2005, 10:12 PM #3
Professional Member
- Join Date
- May 2005
- Posts
- 428
The 42 in the model number means it is a 2-1/2 ton condenser
-
06-13-2005, 10:13 PM #4
Professional Member
- Join Date
- May 2005
- Posts
- 428
i hit the wrong key sorry i mean it is a 3-1/2 ton
-
06-19-2005, 10:35 AM #5
Regular Guest
- Join Date
- Jun 2005
- Posts
- 64
when sizing a/c you down size . when sizing furnaces you up size. say in heating its found you need 84,ooo btus. your furnace choice would be an 80 or 90,ooo. you would need the 90. in ac if you need 2.8 tons of cooling youd install a 2 1/2 ton over a 3. the downsized coil will remove more humidity than the higher one cause the larger one will satisfy the stat faster not giving as much time to condense the water out of the air
-
06-19-2005, 07:24 PM #6
Professional Member
- Join Date
- Feb 2004
- Posts
- 2,597
he's full of ****.
bryant/carrier certaintly come in half ton sizes.
-
06-19-2005, 07:49 PM #7
The 2 stage evolution puron doesn't come in a 3.5 ton.
Did he do a load calc, to see if your old unit was the right size.
If your house needs 3.5 ton, then putting in a 4 ton 2 stage is ok, with the proper duct alterations.
If he didn't do a load calc, and refuses to do one keep calling contractors.
Other manufactures also have 2 stage heat pumps.
Don't get stuck on brand name.


Reply With Quote