    I have a 13 yr old Rheem system that has failed. It is an electric heat pump outside unit model is RPGC-042JAS. What ton size is it and a contractor wanted to replace it with a 3 ton Bryant Evolution series with puron. Should it be a 3 or 4 ton. He said Bryant doesn't come in half tons. Please help with info.The old system worked fine in the summer and a little cool in the winter months.Hard time keeping up on cold windy days.SHOULD HE BEING GOING DOWN TO A 3 TON UNIT?

    [Edited by john3an3 on 06-13-2005 at 10:24 PM]

  2. #2
    Join Date
    Sep 2004
    Posts
    172
    looks like 3 1/2 ton, how is your new contractor coming with his load calculation?

  3. #3
    Join Date
    May 2005
    Posts
    428
    The 42 in the model number means it is a 2-1/2 ton condenser

  4. #4
    Join Date
    May 2005
    Posts
    428
    i hit the wrong key sorry i mean it is a 3-1/2 ton

  5. #5
    Join Date
    Jun 2005
    Posts
    64
    when sizing a/c you down size . when sizing furnaces you up size. say in heating its found you need 84,ooo btus. your furnace choice would be an 80 or 90,ooo. you would need the 90. in ac if you need 2.8 tons of cooling youd install a 2 1/2 ton over a 3. the downsized coil will remove more humidity than the higher one cause the larger one will satisfy the stat faster not giving as much time to condense the water out of the air

  6. #6
    Join Date
    Feb 2004
    Posts
    2,597
    he's full of ****.

    bryant/carrier certaintly come in half ton sizes.

  7. #7
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,566
    The 2 stage evolution puron doesn't come in a 3.5 ton.

    Did he do a load calc, to see if your old unit was the right size.

    If your house needs 3.5 ton, then putting in a 4 ton 2 stage is ok, with the proper duct alterations.

    If he didn't do a load calc, and refuses to do one keep calling contractors.

    Other manufactures also have 2 stage heat pumps.

    Don't get stuck on brand name.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event