just replaced condensing unit with suction line filter.At service valves head pressure 180,suction pressure 90.Air-flow in evap coil fine in and out.In 78 out 74,outside ambient 85.Humidity 50%.Superheat almost non-existent.Suction line at outside unit very cold to touch and sweating profusely.Fixed oriface metering device.New house construction.Last outside unit lasted one month and had a severe burn-out.Fosgene gas in the extreme while replacing.Double checked my gauges and ok.Is this a metering device issue-oversized?-or could it be an inproperly charged issue?I'm new and I can't figure why I have such a low temp split along with abnormal low/high pressure readings.No temp diff across suction filter.
-
06-11-2005, 10:10 PM #2
http://www.hvac-talk.com/vbb/showthr...1&pagenumber=3
scale on second post
-
06-11-2005, 10:20 PM #3
Are you putting in the same brand and size condenser as you removed.
Pump the unit down and check the piston, to see if it is the right size.
-
06-11-2005, 10:22 PM #4
Are you still doing paper work?
-
06-11-2005, 10:43 PM #5
Member
- Join Date
- Mar 2003
- Posts
- 1,877
0 degrees superheat, high suction, low head. looks like
oversized orfice or oversized coil with overcharge. next time give us subcooling.
remember subcooling superheat and pressures = correct answere.
-