    air handler in attic sweating a little around the drain nipples and dripping into drain pan under handler and the first couple feet of condensation line drains are sweating?

    Normal???

    [Edited by mikeinva on 06-10-2005 at 10:23 AM]

  2. #2
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    My guess is low air flow,based on your post about noise,could be causing that as well.

    What's the temp.in and out of the airhandler??


    Can anyone post the "fan data" chart for the OP's appolo not water air handler and the PD of the Rheem coil when wet.


    My guess is the fan in the air handler can't move enough air,with the coil and current duct system.


    What size was the old swystem?Any duct work changed with the install??



  3. #3
    Join Date
    Jun 2005
    Posts
    77
    condenser and air handler same brands and same capacities as old units. ducts replaced with new R6 but all same size.
    72 degree return air into airhandler and 55 degree air from air handler four feet out into supply plenum.

  4. #4
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Possibly overchared ,may still have weak air flow,ducts may be more restrictive then the old ducts.

  5. #5
    Join Date
    Feb 2005
    Location
    Alabama
    Posts
    534
    Need to insulate the first 6 feet (minimum) of that drain line to prevent ceiling damage.
    "If you can't fix it, don't break it."

  6. #6
    Join Date
    Mar 2005
    Location
    NC
    Posts
    230
    I agree with duct dr, insulate the drains for the first couple of feet. The attic is hot and humid, the water that is condensation off the coils is in the 50* range. So you have that cold water flowing out the drain and some staying in the trap. It is normal, but you can insulate it to cure it.

  7. #7
    Join Date
    Jun 2005
    Posts
    77
    Thank you. I appreciate the help.