    Few days ago, I felt no cool air came out of vent, but after while (lot longer then it should be) it seemed to working fine. Yesterday, same thing happened again. Everything seemed to be working just no cool air. I ended up with turning it off. This morning I found something new, when I turned AC on and the outside unit is even spining at all. Then I noticed that the Pepco box (for energy saving)has a little light on. I assume that is when it is working although it should only work during the daytime on extrem hot weather. Anyhow, this might be a separate issue. So, my questions is what could be the problem (intermittent cool air)? And how do I diagnose this issue? This is a 14 years old equipment, worked great.

  2. #2
    Join Date
    Apr 2003
    Location
    Eugene, Oregon
    Posts
    1,209
    While using your refer gauges what pressures did you note while the "no-cool" situation was happening? How about your superheat/sub-cooling, what was that reading? When it was running fine what were your psi readings and superheat/sub cooling measurements?

    When was the last time you replaced your filters or had the equipment serviced?
    Proud supporter of Springfield Millers and Oregon Ducks.

  3. #3
    Join Date
    Jun 2005
    Posts
    3

    No such gauges

    Well I don't really have those fancy tools. But if this is intermittent problem, can I say there is no leak of refregant problem? So, that leads to other possibilities - compressor. How can I tell if it is working or not while condenser's fan is on? Or is there any weak parts can be replaced in compressor that possiblely malfunctions? I don't recall this unit ever being serviced. I should replace filter more often, but will it cause the system totally down or just make it inefficient? Thanks for the reply.

  4. #4
    Join Date
    Apr 2003
    Location
    Eugene, Oregon
    Posts
    1,209
    The tools needed to do proper diagnostics aren't fancy just necessary. There are no parts to replace in a hermetic compressor. Checking amp draw from the compressor while running will tell you basically that it is in fact running, high amp draw or low amp draw will tell you how hard its working but thats about it. Clean filters and clean indoor and outdoor coils will make a difference. Many can be fooled by dirty coils and pump a bunch of refrigerant into the system. You should call a pro and at the very least have you equipment serviced. Good luck.
    Proud supporter of Springfield Millers and Oregon Ducks.

  5. #5
    Join Date
    Jun 2005
    Posts
    3
    Thank you very much, those are very good points.

  6. #6
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    Originally posted by diyfan
    Then I noticed that the Pepco box (for energy saving)has a little light on.
    Congratulations, you have diagnosed your problem!
    Is the kickback on your electric bill worth intermittantly not having cooling? If not, have the stupid thing removed.
    I'm glad we don't have to deal with that crap here.
    If more government is the answer, then it's a really stupid question.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event