Results 1 to 8 of 8
Thread: t.x.v. questions
06-08-2005, 07:47 PM #1
- Feb 2005
- 14
today working on a txv in a walk-in cooler with pump down solenoid valve and txv.
solenoid valve opens and r-22 flows to the valve but nothing thru it, is this normal?
could it be a bad power head? if so, how do i check. or could it be a bad txv valve.?
thanks
06-08-2005, 07:54 PM #2
- Aug 2002
- 6,047
What you do is pump er down and check the inlet screen on the TXV.
Also, it could be a bad power head.
First the screen then the powerhead.
Your on the right track thus far. Keep it simple.
06-09-2005, 12:20 AM #3
You could also put the txv bulb in a cup of hot water and see if it opens up.
06-09-2005, 12:53 AM #4
- Feb 2005
- 14
upon furtherinvestigation i found that the cap tube wore through on the power head. would that keep the r-22 from flowing?
06-09-2005, 12:56 AM #5
- Feb 2005
- 14
i did check the inlet screen when i diesected it. the screen was clean. also id used a lighter to haet the bulb while i had the power head off. would i see that little disk looking plate move? iwould imagine so. or do i have to cool it to see it move??
06-09-2005, 12:58 AM #6Yes, now there is no opening forceOriginally posted by 357
06-09-2005, 01:13 AM #7
I just read your follow up question. I suggest you get some info from Sporlan on how txv's operate.
06-09-2005, 09:07 AM #8
- Feb 2005
- 14
10-4 to that. just have not had to get involved with txv's b-4. with this site it has been helpfull. i have determined that it is a bad power head due to the rub through on the cap tube. thanx again.