    I just got back into the business after four years in the Marine Corps. Before I went in I did alot of service on Furnaces but not to much on A/C

    My question, I was servicing an GE condensing unit today. I put my gauges on and started up the unit, it ran for about 30 seconds before the high side temp got to about 375 and it shut itself off. Any suggestions on what could be the problem? Suction side was 65.

    Model number TA942H1A
    Serial number 214006836

    I thought it was an airflow problem, I cleaned the condesing unit and changed the filter and still had the same problem. Thanks for the help.

  2. #2
    Join Date
    Sep 2004
    Posts
    172
    eddy let me be the first to say thanks for your service to our country and welcome back. On your condensor problem if you have eliminated airflow across the condensing coil as the problem then immediatley check the airflow across the evaporator after that has been eliminated do a superheat and subcooling test and post results. You may have inherited a system that has low evap airflow and has been severly overcharged by someone trying to get the low side up or you could have a high side restriction. Is this a TXV or fixed orfice expansion device type system?

  3. #3
    Join Date
    Jan 2005
    Location
    daytona florida
    Posts
    76
    take a look at the age ge??
    cap tube distrabution??

  4. #4
    Join Date
    Jun 2005
    Location
    Wisconsin
    Posts
    5
    Thank you all

    The current home owner has been in the house for over 22 years and the unit was there when he bought the place.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,776
    Restriction some where.

    Bet some one pumped gas in it last year till it cooled again, and now you got the headache.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Jun 2005
    Location
    Wisconsin
    Posts
    5
    After I decide air flow over evap and condensor is good should I just recover the refrigerant, put into vacuum and charge the system myself?

  7. #7
    Join Date
    Jan 2005
    Location
    daytona florida
    Posts
    76
    theres a lot more than that to do

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,776
    Gotta find the restriction, and fix that before recharging.

    Disconnect the indoor blower and run the unit, and watch the frost.

    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Jun 2005
    Location
    Wisconsin
    Posts
    5
    The unit only runs for about 30 to 45 seconds before it shuts off at 375 on high side

  10. #10
    Join Date
    Apr 2003
    Location
    the Great Pacific Northwest
    Posts
    607
    How much subcooling? You've got to have that number to tell anything. Pull a little ref if necessary to keep unit running for reading.

  11. #11
    Join Date
    Jun 2005
    Location
    Wisconsin
    Posts
    5
    I will try these things tomorrow, thank you all again for the help. I will post results