Thread: Rheem part?
-
06-08-2005, 03:37 PM #1
Regular Guest
- Join Date
- Mar 2005
- Posts
- 157
I was called to a rheem mod.# RGLD-100A-AA. The schematic is no longer available at the homeowner's. There was a control attached to the blower housing I didn't recognize. It has a 110v neautral and 110v hot connected to it, {the hot comes from downstream of the fan control}. It also has 24v wires coming from each side of the coil on the combination gas valve. I will be gaining access to an online rheem work site, but not for a couple more days. Anyone know what the control could be? I would like to solve this question this week. Thank-you.
-
06-08-2005, 04:18 PM #2
Regular Guest
- Join Date
- Feb 2005
- Posts
- 344
RGLD 100
From your description it may be one of two controls. A time delay relay (42-22325-02) or a HAL limit (47-21663-01).
Good luck...
-
06-08-2005, 04:29 PM #3
Regular Guest
- Join Date
- Mar 2005
- Posts
- 157
ruud; If I had to guess I would say it was the time delay. If so what is the purpose of the timing? Thank-you.
-
06-08-2005, 04:46 PM #4
Regular Guest
- Join Date
- Feb 2005
- Posts
- 344
RGLD
The TD is a N.O. "on delay make" that is in parallel with the fan temp switch.
Looks like it brings the blower on after a certain delay even though the fan switch has not made.
It was an option on downflow furnaces.
-
06-08-2005, 05:04 PM #5
Regular Guest
- Join Date
- Mar 2005
- Posts
- 157
ruud; That answers my question, thanks. It is a downflow like you said. One more question if you don't mind, why would they put the relay on the blower versus anywhere else?
-
06-08-2005, 05:08 PM #6
Regular Guest
- Join Date
- Feb 2005
- Posts
- 344
RGLD
Beats me....