Results 1 to 6 of 6
  1. #1
    Join Date
    May 2005
    Posts
    13
    Post Likes
    2200 or 2400? With 2 ton Carrier Infinity system which one is the better choice or doesn't it matter?

  2. #2
    Join Date
    Jun 2003
    Location
    Hell Hole Swamp
    Posts
    4,247
    Post Likes
    They are basically the same except for the dimensions, I would use whichever one was the better fit

  3. #3
    Join Date
    Feb 2005
    Location
    Richmond
    Posts
    482
    Post Likes
    The Static Pressure for the 2400 is higher per cfm.

  4. #4
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,630
    Post Likes
    Look at the deminsions compaired to the return opening on your furnace or air handler. Choose based on wich one will require the least transition work to mate up to your furnace or air handler.
    The pressure drop for both is acceptable for a 2 ton system. The 1400 will have a higher pressure drop because it is smaller, but it is likely a better fit.

  5. #5
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Post Likes
    Try to be sure the ducts design ,includes the pressure drop ,of the filter you choose,it often doesn't.


    Example: builders model has "X" size return duct,customer upgrades to better filter,when his house is built,the duct is the same size as the model,and air flow is very low.


    I'd use the larger one ,if space allows,less pressure drop,longer time between changes.

    Example:4 ro 5 ton system,,returns on both sides of the indoor unit,put a filter in each side,instead of using a single return.Costs a little up front,but now you change two filters once a year ,instead of one filter twice a year.Pressure drop is a lot less.All properly sized to make it happen.

    [Edited by dash on 06-08-2005 at 09:58 AM]

  6. #6
    Join Date
    Apr 2005
    Location
    illinois
    Posts
    257
    Post Likes
    What do you think the maximum air flow a Spaceguard 2200 should handle before you should add a filter to both sides of the furnace. I have been told several times that a dual filter set up is for 5 tons and higher. If I am interpreting your post correctly you would consider this set up for 4 tons as well.