Hello,
I had an Infinity system installed about 8 months ago. Right now I'm getting some "suspect" humidity readings on the stat. It is showing 60%RH while my Radio Shack model (not the cheapest one) in close proximity to the Infinity control is showing 47%.
I know there is some +or- in these things, but a 13% variance seems high to me. Honestly the humidity in the house "feels" a lot closer to 47% than it does 60%.
FYI, the temperature readings between the two devices seem to be fairly close.
Should I get the stat checked out???
Thanks!
Cash
-
06-06-2005, 08:24 PM #2
I would.
They may not have sealed the hole in the wall that the wire comes throough.
-
06-06-2005, 09:47 PM #3Is it that important that the hole in the wall be sealed, because mine is not.Originally posted by beenthere
I would.
They may not have sealed the hole in the wall that the wire comes throough.
Thorton
-
06-06-2005, 11:13 PM #4
Regular Guest
- Join Date
- Apr 2005
- Location
- Tampa, Florida
- Posts
- 1,631
VERY important that the wall be sealed, otherwise air from the attic/crawlspace/etc will move past the stat & it'll sense that rather than the actual inside of the house.
-
06-06-2005, 11:16 PM #5Yep, thats it.Originally posted by tpa-fl
VERY important that the wall be sealed, otherwise air from the attic/crawlspace/etc will move past the stat & it'll sense that rather than the actual inside of the house.