    My new house (built in 1997) has a Goodman HVAC unit. Gas Furnace with of course AC unit outside. I have been in the house for only a month and the unit has failed twice. The control panel in the furnace has been replaced twice. I had another tech come out to give me a second opinion and was told that my supply ductwork was wat to small for my unit. He suggested replacing the Goodman with a smaller unit for the 1st floor only and installing a heat pump in the attic for the 2nd floor. 12K is too much for me to spend as the system seems to cool just fine. I have not had a chace to experience the heat yet. The tech said he would not even replace my system without addressing the duct size issue because the system would fail due to over heating. He also said that since the air moves so fast past the coil that the system will not dehumidify properly. I want to replace the whole unit soon just to start fresh. Should I get another opinion or is duct work that is to small really a show stopper.

    Thanks

    Rob


  2. #2
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    From your previous posts,do you now heat the basement?That would get rid of some "excess " air.


    I'd get someone who can test the static,and is very familar with Man. J and D,sizing and duct design.

    Call around and ask for this,and you'll likely find very few will be interested,those are the ones you want to talk to.

  3. #3
    Join Date
    Apr 2005
    Location
    Finksburg, MD
    Posts
    194
    Post Likes
    Thread Starter
    I currently have only one register in the basement going into my office. The rest of the basement will be finished in a few months so I will need a few additional registers at that point.

    What is J and D duct design? I'd like to have some clue when I call around.



  4. #4
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Man. J is load calculation(size system),including the cfms (air flow) needed for each room in the home.


    Man.D is to design(size correctly) all the ducts ,so each room will get the cfms needed to maintain the temperature evenly.

    Both are products of ACCA,you might want to vist there website.

    Static is thre resistance of the duct system to air flow,Ask to have the ESP,External Static Pressure of the duct system ,tested and compared to the furnace mfrs.. fan data chart.

    High ESP,will give you lower than required cfms,which will shorten the life of your system,and cost more to operate.

  5. #5
    Join Date
    Jun 2005
    Posts
    64
    Post Likes
    what size duct? how many heats?

  6. #6
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    We are accused many times of having a lot of balls on this forum, but none of us have crystal ones. What is size of the house? The furnace? The condenser? The ducts?

    Here's how it works; you give us information and we can give you answers.
    Training is important!
    Practical Training is a must!

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •