    Quote Originally Posted by JBonham27 View Post
    And yes it is all being run off one 3 ton unit downstairs and on the opposite side of the house as the addition. And to be clear, the addition is the only part of the house that is upstairs. I cant tell how old the air handler is because the cover has rusted off. Looks very old but the outdoor unit is from 2005. Very strange.
    So what you're saying is you have 1800 sq. ft. of living space with a 3 ton A/C? I guess it depends on the particulars, but seems a little oversized to me. I would suggest having a load calc done before purchasing any new equipment. I would also look into a heat pump as well, your climate is well suited for a heat pump.
    Quick reply to this message Reply  

  2. #22
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    4,184
    Post Likes
    Inspectors don't know anything about duct, all they are hired to do is make sure its hooked up.

    Without seeing your house nobody here can have a clue about your needs. You need to find a local contractor that knows what they are doing to do an onsite analysis.

    If I came out to your house I would give you a quote to 100% solve your problems and it would not be cheap. Chances are from your post I would probably walk away. the reason is 100% solutions cost 100%. When you start talking about "if we just did this...." then 99 times out of a 100 "I thought it would work better than this?"....and its another "warranty call" to tell you that you should have took the big number. There are plenty of cheap contractors out there to give you partial solutions-look on craigslist.
    I wish I had a $1.00 for every response I deleted.....

    "Decidedly Superior in a twisted pathetic way".....
    Quick reply to this message Reply  

  3. #23
    Join Date
    Feb 2011
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by beshvac View Post
    Inspectors don't know anything about duct, all they are hired to do is make sure its hooked up.

    Without seeing your house nobody here can have a clue about your needs. You need to find a local contractor that knows what they are doing to do an onsite analysis.

    If I came out to your house I would give you a quote to 100% solve your problems and it would not be cheap. Chances are from your post I would probably walk away. the reason is 100% solutions cost 100%. When you start talking about "if we just did this...." then 99 times out of a 100 "I thought it would work better than this?"....and its another "warranty call" to tell you that you should have took the big number. There are plenty of cheap contractors out there to give you partial solutions-look on craigslist.
    I simply posted a question - check the subject line. People started asking other things so i tried to fill them in. I've had more than 5 contractors come out and everyone of them has said something different so I have no clue who to believe or use. And ive heard quotes that are up to 8 grand different so I decided to go to the internet. Are you suggesting I go to the one that is 8 grand more because the cost is 100%. Give me a break. This is an HVAC forum so it seemed like as good a place as any to get some information.

    And isn't that a contactor's job? To offer solutions. Or is there only one in every situation?
    Quick reply to this message Reply  

  4. #24
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    4,184
    Post Likes
    Quote Originally Posted by JBonham27 View Post
    I simply posted a question - check the subject line. People started asking other things so i tried to fill them in. I've had more than 5 contractors come out and everyone of them has said something different so I have no clue who to believe or use. And ive heard quotes that are up to 8 grand different so I decided to go to the internet. Are you suggesting I go to the one that is 8 grand more because the cost is 100%. Give me a break. This is an HVAC forum so it seemed like as good a place as any to get some information.

    And isn't that a contactor's job? To offer solutions. Or is there only one in every situation?
    Yes....but in a previous post you can't even describe the ductwork to the room.. You need a manual J calc to determine how much cfms are needed to be supplied to the room; Will 3 tons cool a tiny room?-YES Will it do it with comfort?-NO Will it do it efficiently?-NO of the contractors ho came out-who actually did a manual J? or would do one and prove their design?
    I wish I had a $1.00 for every response I deleted.....

    "Decidedly Superior in a twisted pathetic way".....
    Quick reply to this message Reply  

  5. #25
    Join Date
    Feb 2011
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by beshvac View Post
    Yes....but in a previous post you can't even describe the ductwork to the room.. You need a manual J calc to determine how much cfms are needed to be supplied to the room; Will 3 tons cool a tiny room?-YES Will it do it with comfort?-NO Will it do it efficiently?-NO of the contractors ho came out-who actually did a manual J? or would do one and prove their design?
    Thanks for answering my question. No one did a manual J calculation. Guess I'll call a couple more.
    Quick reply to this message Reply  

  6. #26
    Join Date
    Feb 2011
    Posts
    75
    Post Likes
    When it comes down to it there really is only one 100% solution. There are practices and methods for sizing ducts and equipment that are very specific. A contractor should be able to come into your home, take all the measurments, and tell you what the "right" way is to condition the house. That solution will be 100% and you will pay 100%. Any other solution is going to leave you less than 100% comfortable and be less efficient.

    Between you and your contractor you have to find the balance between your budget and comfort needs. Just because there is only one correct solution for the home does not mean that it is necesarily right for you. Just know going in that your contractor can do whatever you want them too, as long as you know if may not be 100% correct
    Quick reply to this message Reply  

  7. #27
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    I don't think there is any such thing as a 100% solution. Kind of like reaching absolute zero.

    Let us know the results of your audit?

    Equipment sounds grossly oversized. This leads to short cycling, which means far areas never receive conditioning. Does your ac ever run continuously?

    A mini split works great in small spaces, if duct constraints make one unit impractical.

    Hopefully this free audit will give you an analysis and recommendations regarding the improvements you hope to make. Please share.
    Quick reply to this message Reply  

  8. #28
    Join Date
    Feb 2011
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by tedkidd View Post
    I don't think there is any such thing as a 100% solution. Kind of like reaching absolute zero.

    Let us know the results of your audit?

    Equipment sounds grossly oversized. This leads to short cycling, which means far areas never receive conditioning. Does your ac ever run continuously?

    A mini split works great in small spaces, if duct constraints make one unit impractical.

    Hopefully this free audit will give you an analysis and recommendations regarding the improvements you hope to make. Please share.
    Have a guy from GA Power coming out at noon today for audit so I will let you know. Thanks.
    Quick reply to this message Reply  

  9. #29
    Join Date
    Mar 2011
    Posts
    60
    Post Likes
    the best thing about doing a manual j calc is from that point every dollar spent to fix the problem is moving in the right direction no guessing you may find out a good result is not achievable do to limits on duct size then there are always other options
    Quick reply to this message Reply  

  10. #30
    Join Date
    Nov 2008
    Location
    Chapel Hill, NC
    Posts
    1,070
    Post Likes
    You could use your old 3 ton in the 600 sq ft room. It would certainly cool the room but it wouldn't dehumidify it very well. Also, because it's so oversized, you would have air basting from the vents. Finally, it wouldn't be very a efficient solution. This biggest downside to your proposal, though, is that it wouldn't be cheap - the labor (half the cost of a new install, at least) would be more than you would want to spend to have a half-baked solution to your problem. I'd go with the new HP downstairs and window units until you can afford a 1.5 ton split system or a minisplit.
    Quick reply to this message Reply  

  11. #31
    Join Date
    Jun 2010
    Location
    Western Nebraska
    Posts
    246
    Post Likes
    Quote Originally Posted by JBonham27 View Post
    I also don't plan to live in this house for more than a couple years and do not think I'd get back what I'd put into adding a separate unit.
    Imagine walking into a house in July with a realator and finding the upstairs bedroom is 20 degrees hotter than the rest of the house. Would you buy it?
    Quick reply to this message Reply  

  12. #32
    Join Date
    Jan 2010
    Location
    Texas
    Posts
    159
    Post Likes
    Quote Originally Posted by JBonham27 View Post
    Yes, I know it is not ideal to tap into downstairs but to buy a separate unit for one room upstairs just is not settling well with me. I also don't plan to live in this house for more than a couple years and do not think I'd get back what I'd put into adding a separate unit. I have brought up the minisplit and they all have said its possible but don't see a a great place to mount it. The upstairs bedroom has 6 windows - basically covering all of the exterior wall space.

    How do I go about setting up an energy audit and what would I do with the results?
    Thanks.
    You have a couple choices Follow the advice of the 5 contractors that have seen the job or add supplemental air , as suggested a mini split or since it has so many windows add a window unit or a PTAC ( motel type unit )
    Quick reply to this message Reply  

  13. #33
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Quote Originally Posted by sktn77a View Post
    You could use your old 3 ton in the 600 sq ft room. It would certainly cool the room but it wouldn't dehumidify it very well. Also, because it's so oversized, you would have air basting from the vents. Finally, it wouldn't be very a efficient solution. This biggest downside to your proposal, though, is that it wouldn't be cheap - the labor (half the cost of a new install, at least) would be more than you would want to spend to have a half-baked solution to your problem. I'd go with the new HP downstairs and window units until you can afford a 1.5 ton split system or a minisplit.
    Well put. Only thing I'd add; expect mold, on the supply grilles at the very least. Next on books/paper, and possibly on walls.

    In humid environments it is very important that moisture be removed as air is cooled. Cool it too fast and moisture removal can't keep up.
    Quick reply to this message Reply  

  14. #34
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Have current system replaced with a heat pump. Have contractor dispose of current system. Go to Wal Mart and buy a 4,000 or 5,000 BTU window A/C for that room above the car port. Money well spent, and money saved.
    Quick reply to this message Reply  

  15. #35
    Join Date
    May 2011
    Location
    charlotte nc
    Posts
    93
    Post Likes
    call a pro
    Quick reply to this message Reply  

  16. #36
    Join Date
    May 2007
    Location
    Dry as a bone Tucson
    Posts
    4,866
    Post Likes

    15 tons 460 squares

    Quote Originally Posted by JBonham27 View Post
    Before you think I'm crazy, listen to my scenario. a terrible idea?

    .

    I just bid a job that is going to be 15 tons on 460 sq. ft. There is already 5 tons on it, I'm going to add 10 for redundancy.
    "I aint going to spit on 30 years of my life" Monte Walsh

    Quick reply to this message Reply  

  17. #37
    Join Date
    May 2011
    Posts
    21
    Post Likes
    As others have said...

    Install two units.

    Based on your description you have two separate buildings that are connected. The duct work that was added for the addition is clearly not working, fixing it will likely be more expensive than installing a separate mini-split on the addition.

    So...

    Install a properly sized heat pump in the original part of the home, sealing off the crippled duct work going to the new addition as part of the install. Then install a properly sized mini-split heat pump on the newer addition and call it done.

    Best Regards,
    Mac
    Quick reply to this message Reply  

  18. #38
    Join Date
    May 2011
    Location
    tallahassee,fl
    Posts
    380
    Post Likes
    Unfortunatly sounds like the addition was done wrong to begin with. Heat gain and ducting problems. Energy audit will help determine heat gain problems. Has this problem always existed? 3 tons is way too big don't do it. If reducting isn't possible than seperate cooling source is nessasary ie window unit,ptac or mini split. Zoning won't help unless duct is corrected. Also if seperate unit is used than main unit size will need to be reduced less the 600sqft. Surely 5 techs can't all lack the ability to give good counsel. If the consensus is the same go with it.
    Quick reply to this message Reply  

  19. #39
    Join Date
    Oct 2012
    Posts
    20
    Post Likes
    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 10-24-2012 at 07:47 PM. Reason: non AOP member
    Quick reply to this message Reply  

  20. #40
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    just guessing i would go with a 2 stage unit with zone control and a rehab of the duct system,will probably need a bypass damper . also if you knew how many people say they are moving in a year or 2 to still be there 5 years later .
    Quick reply to this message Reply  

Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •