Results 1 to 7 of 7
    Florida
    Confused
    Ruud 3 ton straight cool with heat strips. This unit is for my Garage/shop. The contactor had the dreaded ant across the contacts and burned the contactor up. I replaced the contactor and now have nothing unless I manual momentarily push the contactor in by hand. I have checked the t-stat and even replaced it with a known good one, but no luck. Today I got in the attic and used the volt meter to check the control transformer. I had 240 volts in on the correct taps for input and nothing on the re coming out..... Guess that means a trip to the parts house. Could the ct have gotten trashed by the contactor having arced around the ant that was in there making it chatter?? Never had a bad ct before...
    Nov 2003
    You probably blew the low voltage control fuse when you were doing the contactor.
    Florida
    I do not see a fuse on the lo voltage circuit. Where in the air handler would it be?uud unit and did not see it on the schematic...
    Florida
    Also would I still get no votage right at the transformer even though I have 240 going in????
    Jan 2003
    Transformer is dead. A lot of unit don't have fuse. You might want to install a fuse.
    burlington county n.j.
    if contactor had fried coil it would almost always wipe out transformer,if there was no fuse in low voltage circuit.
    Florida
    Thumbs up
    All fixed now!! It was the control trans. Only time I had to replace one. Imagine that, living in the lightning capitol of the world!!!