wire size
Nordyne Package P5RD-036k w/ 10kW heat strip MCA 52 amps MOP 60 amps recommended wire size #8 shouldn't it be #6
-
03-09-2011, 09:38 PM #2
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,211
who recommends # 8
it'll work, not necessarily the preferred wire size
i believed in pulling to the max, fuse to the minimum.....
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
03-09-2011, 09:41 PM #3
New Guest
- Join Date
- Mar 2011
- Posts
- 3
OEM install guide
-
03-09-2011, 09:53 PM #4
Professional Member*
- Join Date
- Dec 2003
- Location
- Citrus County, Florida
- Posts
- 1,231
do a google search for ampacity. You can pull 55 amps with #8
Doug
-
03-09-2011, 09:59 PM #5
Professional Member*
- Join Date
- Apr 2009
- Location
- Pan Handle, Fl
- Posts
- 597
60 Amp requires #6
Breaker size is suppose to match wire amp rating. 60 amp breaker requires #6 wire.
Insanity: Doing the same thing over and over again expecting a different outcome!
-
03-09-2011, 10:00 PM #6
Regular Guest
- Join Date
- May 2010
- Posts
- 1,289
Use #6. You can always go bigger but not smaller. Go too big and the lug won't accept the wire size. With a 60amp breaker you should never go smaller than a #6 EVER!
-
03-10-2011, 11:23 AM #7
Professional Member
- Join Date
- Mar 2011
- Location
- Jamestown,SC
- Posts
- 45
I would go with a 6. If you ever added 5 kw you would still be safe. A heavier wire will also make it easier to sleep at night.....
-
03-10-2011, 08:31 PM #8
Regular Guest
- Join Date
- May 2009
- Posts
- 520
It really depends on the quality of the wire (amount of insulation it has around it)
-
03-10-2011, 08:40 PM #9
Master Electrician here, # 6 SEC or THHN, number 6 NM is only rated for 55 amps.
-
03-11-2011, 10:46 AM #10
Regular Guest
- Join Date
- Jul 2008
- Posts
- 550
That is only if both the terminals on the breaker and equipment are 90C rated.
#8 AWG is OK if all the requirements are met (assuming 52A load/min circ rating). The terminals need to be 90C rated and the wire must be 90C rated. For copper wire it needs to be something like THHN, THHW, THW-2, THWN-2, etc as per table 310.16 in the NEC. Also make sure none of the run is exposed on a rooftop.
-
03-11-2011, 11:06 AM #11
Regular Guest
- Join Date
- Nov 2008
- Location
- SW Florida
- Posts
- 20
-
03-11-2011, 11:51 AM #12
-
03-11-2011, 02:35 PM #13
Regular Guest
- Join Date
- Jul 2008
- Posts
- 550