Results 1 to 3 of 3
  1. #1
    Join Date
    Jun 2005
    Posts
    2
    Post Likes
    Hi, we have just bought our first house and have a question. The house is six years old and we are in NY state.
    We have a Heil DC90 furnace, with humidifier attachment but no A/C.
    The thermostat is a Maple/Chase 09600, electronic, heat/cool. There is a separate humidity controller.

    We were looking into wiring up the fan only option (thermostat manual shows wiring diagram for it, wire running from there to furnace is three core, furnace has a connector for it) but at the moment only the red and white wires are used, the green is wound around the wire and not connected. Is this because of the humdifier?
    Any ideas why this is not connected and is it safe (and a good idea) for us to connect it?

    Many thanks in advance for any info.

    Bob
    ps did a search but do not think I am good at them as I rarely find the info I need.

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    35,210
    Post Likes
    Shut the power off at the furnace, connect the green wire to G and both the stat and the furnace control and you'll have a blower when in the on position.

  3. #3
    Join Date
    Jun 2005
    Posts
    2
    Post Likes
    I was thinking that would work, but wondering why they didn't do it during the installation, seems such an easy way to make the system more functional!