Results 1 to 10 of 10
    Jan 2005
    Littleton, CO
    Question
    I'm trying to find the trouble codes for a Carrier Furnace Model # 58PAV090-14. Does any one have any idea where I could get these codes? Thanks.
    Houston,Tx.
    Willis Haviland Carrier has a bunch of folks that can help you call 1-800-CARRIER (1-800-227-7437).
    Apr 2004
    Midwest
    What fault are you looking for?
    Try Carrier.com they have tons of good info there...
    Live each day like it is your last, for one day you will be right!
    carrier fault codes
    You may try (www.hvactechsupport.com) They have some info. on carrier units.
    11 NO PREVIOUS CODE - Stored status codes are erased when power (115V or 24V) to control is
    interrupted or 48 hours after each fault is cleared.
    12 BLOWER ON AFTER POWER UP (115V or 24V) - Blower runs for 90 seconds, if unit
    is powered up during a call for heat (R-W closed).
    13 LIMIT OR FLAME ROLL-OUT SWITCH LOCKOUT - Auto reset after three hours. For flame
    roll-out switch or fuse link, refer to #33.
    14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
    21 GAS HEATING LOCKOUT - Control will NOT auto reset.
    Check for: - Stuck gas valve relay on control or miswire to gas valve circuit.
    22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
    de-energized. Inducer will run until fault is cleared. Check for:
    - Stuck-open gas valve or leaky gas valve.
    23 PRESSURE SWITCH DID NOT OPEN Check for:
    - Obstructed pressure tubing. - Defective pressure switch (stuck closed).
    24 SECONDARY VOLTAGE FUSE IS OPEN
    Check for: - Short circuit in secondary voltage (24V) wiring.
    31 PRESSURE, DRAFT SAFEGUARD, OR AUXILIARY-LIMIT (when used) SWITCH DID
    NOT CLOSE OR REOPENED - If open longer than five minutes, inducer shuts off for
    15 minutes before retry. Check for:
    - Proper vent sizing and condensate pitch. - Inadequate Combustion air supply.
    - Vent restriction or high winds. - Low inducer voltage.
    - Defective inducer motor or start capacitor. - Disconnected or obstructed pressure tubing.
    - Defective pressure switch or connections. If it opens after trial for ignition period, blower will
    come on for 90 second recycle delay.
    33 LIMIT OR FLAME ROLL-OUT SWITCH IS OPEN - If open longer than three minutes, code
    changes to #13. Check for:
    - Defective blower motor or start capacitor. - Dirty filter or restricted duct system.
    - Loose blower wheel. - Defective switch or connections.
    - Inadequate Combustion air supply Flame Roll-out Switch or fuse link.
    - Open Flame Roll-out switch,or fuse link. Manual reset or replace.
    34 IGNITION PROVING FAILURE - Control will try three more times before a lockout #14
    occurs. If flame signal lost after trial for ignition period, blower will come on for
    90 second recycle delay. Check for:
    - Oxide buildup on flame sensor (clean with fine sandpaper).
    - Proper flame sense microamps (.5 microamps D.C. minimum).
    - Gas valve turned off. - Manual shut-off valve. - Low inlet gas pressure.
    - Green wire MUST be connected to furnace sheet metal.
    - Inadequate flame carryover or rough ignition.
    COMPONENT TEST
    To initiate the component test sequence,shut OFF the room thermostat or disconnect the "R"
    thermostat lead. Briefly short the TEST terminal to the ’C’ terminal. Status LED will flash code and
    then turn on the inducer motor, hot surface igniter, blower motor-heat speed, and blower motor-cool
    Apr 2003
    California
    WOW , did you bring the whole furnace door into your computer room or what? just kiddin,,
    Apr 2004
    Midwest
    dj is much more dedicated than me! LOL
    No way would I have typed all that out!
    Jan 2005
    Littleton, CO
    Smile
    DJKEN, and everyone else thanks for all your input. This is going to help me a lot.
    See next Post...
    See Post Below...
    [Edited by AllTemp on 06-05-2005 at 11:40 PM]
    AllTemp Heating & Cooling
    Re: 58PAV Installation/Service Manuals
    [QUOTE]Originally posted by AllTemp
    [B]
    Below are links to the Service and Installation manual for this furance. Just click on the link....
    Requires Adobe Acrobat to read...
    You can save these files for future use or just print them out as a manual.
    I catalog all my PDF files, sure comes in handy such as moments like this...
    http://www.alltemp-hvac.com/58p,r-15sm.pdf
    http://www.alltemp-hvac.com/58pa-15si.pdf
    [Edited by AllTemp on 06-05-2005 at 02:27 PM]