    Can anybody give me any information on calculating or requirements of combustion air on a wood burning firplace?
    Thanks!
    Live each day like it is your last, for one day you will be right!
    Midwest
    Nothing? LOL
    Jan 2011
    Huntley, IL
    You will have to back into it...
    First, check with the stove/fireplace manufacturer.... if that doesn't work, try below.
    It depends on the size of your stove/fireplace and how much wood you burn.
    I found this website (two links) to be very useful:
    http://www.chimneysweeponline.com/howood.htm
    at the bottom of that page it shows how he derived these numbers:http://www.chimneysweeponline.com/howoodbtu.htm
    From the example given on the second link, a 1 lb. of Osage Orange would be equal to 8660 btu which if used to develop combustion air calculation, would be conservative/safe. The other two numbers given with moisture content would be more realistic, but less safe.
    Once you know how many BTU's your stove/fireplace would burn you can calulate the indoor combustion air at 50 cubic feet/1000 btu of wood being burned or vent openings of 2 square inches/1000 btu with a minimum of 100 square inches for each of the two required openings (IFCG 304.5).