Results 1 to 9 of 9

Thread: screws into B-Vent?

  1. #1
    Join Date
    Jan 2005
    Location
    Columbia, Mo GO, TIGERS
    Posts
    935
    Post Likes
    the manufacturer of the brand we use says in their
    instructions don't put ANY screws into their nice shiny metal B-vent.
    Obviously, this makes supporting the flues a bit trickier.
    An old-timer in our outfit says the mfg is just covering
    their butts...that if one uses short enough screws to
    NEVER pierce the liner a few screws are ok. He claims, beyond
    the obvious problem of a hole being a potential flue gas leak, that
    when a too-long screw is in contact with both the liner and the
    outer shell it sets up galvanic corrosion and the liner
    can erode pretty quickly into powder.
    Thoughts, anyone? How do you'uns support flues when they can't go straight up?

  2. #2
    Join Date
    Jun 2001
    Location
    Tx
    Posts
    3,917
    Post Likes
    Plumbers tape tightly wrapped a couple of times and then screwed to 2 joist.

  3. #3
    Join Date
    Nov 2004
    Posts
    125
    Post Likes
    We used screws for years in B vent, but now are using friction clamps where possible to support.

  4. #4
    Join Date
    Nov 2003
    Posts
    504
    Post Likes
    Our local codes require us to screw the B-Vent, but ONLY with 3/8" screws. They say it won't pierce the inner liner, but I've seen it happen on some pieces.

  5. #5
    Join Date
    May 2004
    Location
    Rapid City, SD
    Posts
    7,414
    Post Likes
    I never really have the need for anything like that. We screw the single wall pipe to the bvent, sometimes throw a couple screws in the chimney top. But for supporting we typically let the ventfast do that for us.

  6. #6
    Join Date
    Aug 2002
    Location
    Cincinnati, Ohio
    Posts
    3,439
    Post Likes
    The whole screws in B-Vent has to do with the fire rating. The air space between the two walls provides for clearance to combustible materials. The joints make contact(inner wall with outer wall) so there is minimal fire rating so screws have little affect. One manufacturer told me that if you install his B-vent the #@%&*!@ way it won't come apart but srcews are okay. Screws cannot be used to seal holes in B-vent when we do combsution testing. This does transfer heat from inside to outside and messes up the fire rating.
    captain CO

  7. #7
    Join Date
    Jun 2005
    Posts
    64
    Post Likes
    to support offset flues in attics i use a couple long 1x3 angles. overlap the angles about 4 inches and use 2 screws to hold angles together. make 2 snips on the 1 inch bend side 4 inches apart, then bend into an a frame. wrap a frame around flue and squeeze then secure to truss. ill use 1 on the horizontal part and another where exits the roof. very sturdy installation. the roofer can try to push that flue around and wont be able to.

  8. #8
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,434
    Post Likes

    insulation

    Once you've pierced the inner liner, you loose the insulative properties created by the double wall. This is a Dewar's Flask or thermos bottle effect. How well would your thermos be at keeping your coffee warm with a hole in the outer wall?

    Also, once the insulation is lost, you lose fire rating/ clearance as Jim Discussed. It reverts back to a single wall vent connector, which carries a 6" clearance. Without the insulation, you lose heat, which hinders draft. The cooler flue liner also contributes to condensation. If it ever went to court that a CO exposure resulted from a leak in B-vent caused by corrosion because someone put a screw into it, you'd be toast. Have there been cases like this? Who knows? Most companies keep a tight lip on litigation.

    Use the mfrs. supplied supports or recognized field expedient adjuncts such as plumbers straps or drives with stove bolts.

  9. #9
    Join Date
    Feb 2004
    Location
    OK
    Posts
    30
    Post Likes

    screws

    I used to put 3 screws in each joint. One time I looked up a water heater vent I had just screwed together. The screws didn't penetrate the liner, they just pushed it in. This left a big gap where the gases could get up outside the liner. This would probably cause the pipe to corrode quickly. If a joint feels too loose a little hammer work will fix it.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •