    I have a Carrier 58PAV that went out several days ago. Tstat is has no display. There is no 24vac present on the control board. 3amp fuse - good. Verified 120vac going into the transformer primary. 0vac on the secondary output. Replaced transformer with a new one and I get the same condition - 120v in and 0v out. Is it likely I have 2 faulty transformers, or is there something I'm missing?? Any suggestions would be appreciated....

  2. #2
    Join Date
    May 2005
    Posts
    428
    The transformer is going bad for a reason. something in your 24 volt control side of the transformer has probably went to ground, like a bare wire touching metal or two control wires that are bare touching each other. i am taking for granted you are using the proper transformer. you might consider calling a professional because the transformers will keep going out if the problem is not found. good luck.

  3. #3
    Join Date
    Apr 2005
    Location
    Inland Empire,CA
    Posts
    56
    Check your safeties for shorts or ground. I would start with the heating section first (rollout or limit switch). Just a thought.

  4. #4
    Join Date
    May 2005
    Location
    Boston
    Posts
    30
    No fuse on the 24V side?

  5. #5
    Join Date
    Nov 2003
    Posts
    501
    Originally posted by fick
    No fuse on the 24V side?
    ajc3 said -

    3amp fuse - good.

  6. #6
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,761

    Hmm

    gotta buy transformers 6 at a time, sometimes it takes that many to get a good one!!!!!!!!!!